Replacing steam oil boiler with gas
branimal
Member Posts: 228
I’m replacing an old oil steam boiler with a gas boiler. The oil boiler cracked (water spewing out the side) last winter after it was winterized by a boiler technician. Fortunately insurance is covering part of the damage.
I’ve gotten three quotes for the job.
The property is a 3 family, 3 floors + basement and each floor is about 1100 sq ft. 19.75’ x 55’. Attached house (house to the left and right). 3-4 windows in the front and the back on each floor.
I don’t know much about gas boilers …. and from what I’ve read this is not a DIY project at all, so i’m hiring pros.
All 3 quotes are for burnham boilers (independence). IN6 and the IN7. The btu range is as low as 175K and as high as 210k.
How do I know whats right for the space and the existing steam system I have in place?
One contractor (175K BTU) said installing a stainless steel chimney liner may not be necessary. They are going to clean the chimney I’ve read that dangerous gases can seep into the apartments if the chimney isn’t properly lined.
The 2nd contractor says he’ll clean the chimney… but as long as its in good shape, it doesn’t need a liner.
The 3rd contractor is installing a chimney liner.
Any advise on the process will be greatly appreciated.
I’ve gotten three quotes for the job.
The property is a 3 family, 3 floors + basement and each floor is about 1100 sq ft. 19.75’ x 55’. Attached house (house to the left and right). 3-4 windows in the front and the back on each floor.
I don’t know much about gas boilers …. and from what I’ve read this is not a DIY project at all, so i’m hiring pros.
All 3 quotes are for burnham boilers (independence). IN6 and the IN7. The btu range is as low as 175K and as high as 210k.
How do I know whats right for the space and the existing steam system I have in place?
One contractor (175K BTU) said installing a stainless steel chimney liner may not be necessary. They are going to clean the chimney I’ve read that dangerous gases can seep into the apartments if the chimney isn’t properly lined.
The 2nd contractor says he’ll clean the chimney… but as long as its in good shape, it doesn’t need a liner.
The 3rd contractor is installing a chimney liner.
Any advise on the process will be greatly appreciated.
0
Comments
-
First piece of advice I can give you is that we don’t discuss pricing @branimal, so you’ll want to remove that text. Second piece of advise is, did any of the contractors measure the radiators? This is how you determine the appropriate steam boiler size. If none of them did, then award none of them the job. This is step 1.0
-
There is only one way to size a steam boiler: go around the building and add up the EDR of all the radiators. Any other approach is doomed. If any of the folks you have talked to hasn't done that, they're out.
We don't talk price here on the Wall, so it might be well to edit the prices out...
Where are you? We may know a really good steam guy in your area to help you out.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I’m in brooklyn, NY
No one measured the radiators but they all assumed they’d be a certain size.
Ill measure the radiators today. There seem to be some spots where there should be a radiator but none present. Maybe the old owner took them??
I’ll google EDR -thx.0 -
-
-
Brooklyn? A number of good folks around -- check the "find a contractor" tab on this site.
EDR is "Equivalent Direct Radiation" and is a measure of the surface area of the radiator...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Chimney liner depends on what you have already. Some masonry chimneys have clay tile liners that can work well as long as they are in good shape (this is up to the local code officail though, so you may want to check with them). If there is no liner, then you will have to install a flexible stainless steel liner. The reason for the liner is not so much about allowing carbon monoxide into the building, as it is about keeping the carbonic acids that form in the products of combustion from eating away at the lime in the mortar. If this goes unchecked for too long, the chimney will start to degrade and eventually fall apart. Because of the higher stack temperatures and the different combustion chemistry, this is not as much of a concern with oil boilers.
Agree with all of the above, anyone who did not actually size up all the radiators, or who at least did not agree that before the boiler was ordered they would do so to finalize the price, needs to be shown the door.1 -
The most knowledgeable contractor (measured each radiator to come up with EDR number) recommended a Williamson boiler. (Its a Weil-McClain with a different shell). Every other contractor recommended a Burnham.
The one issue I have with this contractor is he does not want to do the job with a permit. Most likely he doesn’t have a license to install boilers. He said National Grid (my gas provider) would not care if my gas bill jumped from $75 (water heater & stove) to $250 (water heater, stove, boiler). For ConEd that’s an automatic red flag. They will shut down the meter and report it to NYC Department of Buildings (NYCDOB). That would be a **** storm. This is not a risk I am willing to take. If for any reason National Grid changed their policies, I’d be up ****’s creek.
I’ve got quotes from two licensed contractors that are within spitting distance of one another. Higher quotes, but they are filing permits. They said they will measure each radiator after I sign contracts and pay a deposit.
I have 3-4 missing radiators in the building. I’m going to have the plumber replace them. Also is it worth replacing the air valves and control valves on each existing radiator?
What boiler bells and whistles should I look into?0 -
-
I would start over with your quotes and have one of the pros on Heating Help get you straightened away. You are lucky that there are a number of excellent contractors right in your area. Guys who are willing to post pics of their installs for everyone else to critique.
Your posts and thought process are just setting off alarm bells that you'll be back in 6 months with problems. No disrespect but that seems the common course when advice is not heeded by the folks here who are only interested in you having a great experience.
I would post in Strictly Steam and see what folks say.Peter Owens
SteamIQ1 -
How are they even giving a quote without knowing even close to what boiler size they need?
This is speculation, but I doubt many that know would disagree with me. I would suggest the boiler size they have quoted is massively over sized for an 1100 sq ft house. For steam it is all about the radiation, but I can't imagine you having that much radiation in such a small house.
If you want to figure the boiler size yourself, we can help with that as it's pretty straight forward. Measure the height and depth of each radiator and count how many sections each one has. Also post a picture of each one. With that information I'd be happy to calculate the EDR for you and let you know what size boiler you should have.0 -
Following up on the replacement of oil boiler with gas boiler. Found a plumber with great ratings on google for heating systems. He’s replacing the boiler KIN-7 steam boiler. Obtaining all the permits, removing the oil boiler & 275 Gallon oil tank. Installing a new header, equalizer, hartford loop, automatic water feeder, low water cutoff, new thermostat.
I’m getting a new meter for the gas boiler and the water heater.
Making the system ready for split system fittings - in case i want to heat the basement.
As far as the chimney liner is concerned… I’ve heard that NYC may require me to have a stainless steel liner, or may not. It depends on the inspector. The clay lining in my chimney is in decent shape. If the inspector deems a liner required I will have to file some form with the city which will cost $$$$. If the liner is in place, I can always say the previous owner had it installed.
I went ahead and had a liner installed. The contractor connected it to the water heater (properly pitched), left a new connection for gas boiler and installed a cleanout. I needed a ovalized duct b/c my boiler requires a 7” diameter, but the flue is 6 1/5/16 x 11.
The liner install seemed like a possible DIY job, but time is of the essence here with temps dropping.
Thanks for the help guys.0 -
To put things into perspective, I have a 1600sqft 150+ year old house with the equivalent of little more than a Burnham IN-4. And my radiation is grossly oversized for the house.KC_Jones said:
He's installing a Burnham IN-7 boiler, in an 1100 sq ft house? Are you positive he sized it correctly? That is a massive boiler for a house that size, as I stated in my previous comment.branimal said:He’s replacing the boiler KIN-7 steam boiler.
I only comment because this is an extremely common mistake made by a lot of contractors.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
-
opps...need to work on my reading comprehension.
0 -
The home is 1100 x 3 = 3300. Plus at some point I'd like some heat in the basement in case I duplex the 1st floor and basement. Common in Brooklyn renovations these days.0
-
> @branimal said:
>
> I don’t know much about gas boilers …. and from what I’ve read this is not a DIY project at all, so i’m hiring pros.
>
Why do I feel just a little insulted by that comment.
I was reading how I could give myself a lobotomy but after the first page I realized I must've done it already.0 -
I'm Brooklyn, I have 37 radiators and they range from 14 to 30, the larger on the top floor where there the risers stop. oh and a 65 in the hallway.branimal said:I’m in brooklyn, NY
No one measured the radiators but they all assumed they’d be a certain size.0 -
Boiler has been replaced with the Burnham KIN7. Installed a 7" ovalized stainless steel flue pipe.
The electronic damper was defective so the plumber left it in "jumped" mode. The plumber will be replacing that soon.
The building is nice and toasty. In fact the tenant is complaining it too hot in his bedroom after he's shut off radiators near his bedroom.
I'm going to drop the temperature from 70 to 68.
Thanks for the advice guys.
@HVACNUT I didn't mean to insult. The main mechanic was a real pro.
1 -
That's a nice installation. I'm glad this worked out for you considering the train wreck that seemed inevitable in your first few posts.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements