setting draft properly on burnham gas fired steam boiler
stevenknaub
Member Posts: 24
Hi, I purchased a Dwyer Mark II barometric manometer. I installed a Field Controls MG1 barometric draft control. This is on a Burnham Independence IN-4 natural draft boiler. (not powered draft). A couple of questions I have:
1. is there a way to measure over fire draft?
2. what is the proper over fire draft?
3. what is the proper draft setting pre-draft control?
4. am I to use the "high" or the "low" fitting on the Dwyer manometer? (does the hose connect to the high or the low fitting?)
5. am I setting to a positive draft per the manometer, or a negative draft? (I have seen alot of contradictory information)
I am hoping you can assist. Is there a video available that may answer all or most questions?
thanks for any help you are willing to provide
1. is there a way to measure over fire draft?
2. what is the proper over fire draft?
3. what is the proper draft setting pre-draft control?
4. am I to use the "high" or the "low" fitting on the Dwyer manometer? (does the hose connect to the high or the low fitting?)
5. am I setting to a positive draft per the manometer, or a negative draft? (I have seen alot of contradictory information)
I am hoping you can assist. Is there a video available that may answer all or most questions?
thanks for any help you are willing to provide
0
Comments
-
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0
-
Should already be a draft hood on that boiler..........All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Think your spinning your wheels. The independence is a natural draft boiler with a draft hood. I wouldn't use a barometric damper with it and there is no need to measure or adjust the draft...............unless you have some type of unusual condition like excessive chimney draft0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements