Cast iron baseboard
Options
bob eck
Member Posts: 930
How many feet of cast iron baseboard can you run on one loop. 3/4” copper M will be run to the cast iron baseboard or should 1” be run to it.
Anyone know what GPM that cast iron baseboard can flow at.
Can 4 GPM be run through the CI baseboard.
Anyone know what GPM that cast iron baseboard can flow at.
Can 4 GPM be run through the CI baseboard.
0
Comments
-
You need to find the max flow rate from the baseboard mfg. 4 gpm is standard. 4 gpm with a 20 degree TD will give you 40,000 btu. Take btu rating/foot at the average water temp you are using.
40,000/btu rating/ft = footage to install0 -
In theory, not more than about 65'. A 3/4" line can carry about 4 gpm or 40k btu at a 20* delta T.
The Baseray manual that I have gives the same two flow rates as fine tube: 1gpm and 4 gpm. So 4 gpm should be possible, but the radiator's output is only slightly higher (450 btus per ft. @170* average SWT).Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements