Need advice for what to do with old, crusty, leaking radiator valve.
When I bought this house last year I discovered that one of the radiator valves has been leaking, seemingly around the union nut. I schmeared some RTV sealant around it, which slowed the leak somewhat, but I just dealt with it for the rest of the winter by keeping a small bowl underneath. Now I'd like to fix this properly. Also this valve wont close all the way, or at least when closed all the way, steam still gets through. I'm thinking that changing this valve is probably the best course of action at this point.
I think this is what I need: https://www.supplyhouse.com/Bluefin-RVST150-1-1-2-FIP-x-Male-Union-Steam-Angle-Radiator-Valve?gclid=Cj0KCQjwlqLdBRCKARIsAPxTGaXbPROy39Tq4FljvSz_9-YAkbt3H_kneOIirz8eU35x42IBQpwd7NoaAnKiEALw_wcB#reviews-content
However I'm concerned about the height of the valve. Based on the pictures alone it seems the new valve is shorter, and I'm concerned there'll be a height mismatch once the new valve is screwed onto the riser.
Also this will be the first time changing one of these valves as I'm new to steam heat, but I've been an auto mechanic for most of my life and at least know which end of the wrench to hold.
Any suggestions? Thank you in advance.
Comments
-
I that looks bad I would replace it
Located in durham NC.
0 -
but you can get a little play with the pipe and get a pot belly valve they tend to last longer
Located in durham NC.
0 -
It does look as though it has been leaking around the union. The first thing to do is to take the union apart and thoroughly clean the mating surfaces and look and see if they are nice and smooth with no scratches or the like. Then try to put it back together. Remember with plumbing unions that the seal is on the mating surface -- not on the thread -- and that they aren't intended to compensate for any significant misalignment. You may find when you take it apart that the feed pipe drops; no problem, so long as you can pull it up again. Make sure that the thing is lined up, and then tighten the union. Do NOT overtighten -- that can crack the nut. You may find that rocking the radiator slightly while tightening helps to get it snug.
Now. Hopefully that fixes the leak at the union.
I can't really tell from the photo, but it doesn't look as though the valve is leaking at the bonnet or the stem, which is good. However, if it really lets a significant amount of steam through, you may want to take the valve apart and check the valve seat. They get tired, but are usually replaceable. If you do, you will need to replace the packing around the stem. Again, when you put it back together the bonnet needs to be snug, but don't reef on it -- only enough so it doesn't leak. They crack really easily.
Now... hopefully you are all set. However...
If you still need to replace the whole valve, you have picked a good enough valve. However, note that it comes with the spud. The spud and the valve are matched. You will have to get the old spud out of the radiator, and that can be a real bear. But you do have to do it; don't even try to replace just the valve.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Are you sure the existing valve is 1-1/2" like the one you linked to?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks for the info. I do know about having to change the spud, and yes it looks like a pain, but I think with careful use of a hacksaw blade and chisel I can manage. I'm more worried about ending up with a height mismatch or worse, damaging the riser pipe.Jamie Hall said:It does look as though it has been leaking around the union. The first thing to do is to take the union apart and thoroughly clean the mating surfaces and look and see if they are nice and smooth with no scratches or the like. Then try to put it back together. Remember with plumbing unions that the seal is on the mating surface -- not on the thread -- and that they aren't intended to compensate for any significant misalignment. You may find when you take it apart that the feed pipe drops; no problem, so long as you can pull it up again. Make sure that the thing is lined up, and then tighten the union. Do NOT overtighten -- that can crack the nut. You may find that rocking the radiator slightly while tightening helps to get it snug.
Now. Hopefully that fixes the leak at the union.
I can't really tell from the photo, but it doesn't look as though the valve is leaking at the bonnet or the stem, which is good. However, if it really lets a significant amount of steam through, you may want to take the valve apart and check the valve seat. They get tired, but are usually replaceable. If you do, you will need to replace the packing around the stem. Again, when you put it back together the bonnet needs to be snug, but don't reef on it -- only enough so it doesn't leak. They crack really easily.
Now... hopefully you are all set. However...
If you still need to replace the whole valve, you have picked a good enough valve. However, note that it comes with the spud. The spud and the valve are matched. You will have to get the old spud out of the radiator, and that can be a real bear. But you do have to do it; don't even try to replace just the valve.
I think so? I held up a ruler to union and eyed it real good. Seems like 1-1/2" to me but maybe I'm looking at it the wrong way?Steamhead said:Are you sure the existing valve is 1-1/2" like the one you linked to?
0 -
Sized are determined by inside diameter.
You can measure the outside circumference with a tailor's cloth tape.
Post that here and someone can tell you the ID.
0 -
I believe Marsh makes valves that are longer and may better match what you have.0
-
If you do decide to change the valve rather than repair it, be aware that you are in for an interesting day. Be careful taking the spud out not to damage the threads in the radiator -- that will scrap the radiator. And be careful in taking the valve off the riser not to twist the riser even slightly. That will cause a hidden leak. It's not fun.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'm starting to think I should call a plumber lol.0
-
@jtor1134
you can do this. I have done a lot of this. Get and angle grinder with some cutting disks.
1. Take a couple of hammers and put one on the back of the union and hold it tight to the union as a back up. Rap the opposite side of the union. You don't have to smash it, just 3-4 good raps. The union should then come loose with some pipe wrenches
2. Move the rad out of the way so you can work on the riser. Measure up from the bottom of the old valve 1", make a mark and take the grinder and cut the old valve off at the mark horizontally. You won't hit the pipe as the old pipe makes in no more than 3/4"
3. Once you cut the valve out make a few vertical cuts in the remaining part of the valve around the circumfrence Don't make the cuts too deep go down to the threads and leave the last 1/8"
4. You can then wrench off the piece or cut it with a chisel as it will be weakened by the cuts.
5. A hacksaw or sawzall used with care can cut the old nipple out of the radiator also with a hammer and chisle
6. Now you got the hard part done.
7. As long as the new valve is reasonably close you can make it fit
8.
Worse case if the new valve is shorter and you can't pull the pipe up put an "extension coupling" ( male x female coupling) on the riser...then the new valve. Then shim under the radiator legs if need be0 -
Your best bet is to fix the old valve. Clean up the mating faces of the Union, as Jaimie advised, and inspect the bonnet, and packing nut while the system is running. If the packing nut shows any sign of leaking, then repack.
Save your money for some good main venting, and a low pressure, (0-3 psi) gauge!—NBC0 -
Got the radiator off. The union nut was surprisingly easy to remove. The mating faces of the union don't seem too bad. No gouges or corroded spots. I'm going to try and clean them up with steel wool and use RTV sealant and put it back together and see what happens.
0 -
Keep the sealant to a minimum -- only a very thin layer!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Use dishwashing liquid on the faces of the union, and rock it from side to side as you tighten it. Don't put sealant on it.--NBC0
-
Success! There’s a plumbing supply store near my house so I went to pick up some steel wool and I asked an old-timer there what I should use as a sealant. He handed me a jar of “real tuff” and told me how to use it. So I polished up the mating surfaces with the steel wool, applied a thin layer of the stuff, nearly threw out my back trying to get everything back together and cranked the union nut good and tight. Ran the boiler and it’s no longer leaking. Of course now it’s leaking from the valve stem but I know how to repack a valve so I’m not worried. I’m just glad I don’t need to change that valve right now. Wasn’t looking forward to that.1
-
just saying i would took the opportunity to patch the floor while the rad was off
Located in durham NC.
0 -
It's actually normally covered by a radiator cover, so you don't see it. I plan on replacing the flooring in the future so I'm not going to bother until then.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements