5 zones, going with zone valves & a Weil McLain 155,000 ultra.
Would you go with the delta t or delta p pump?

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,524
    Options
    P. As zones close down the pump will back down
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    would you go with taco or grundfos
  • Zman
    Zman Member Posts: 7,569
    Options
    Taco or Grundfos is kind of a Ford or Chevy question. They both good brands.
    I do like the support Taco has offered on this site and would select Taco for that reason.
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    if i go with taco shouldn't i just go with a delta T, especially if i use the outdoor reset that comes with the ultra.
  • hot_rod
    hot_rod Member Posts: 22,142
    Options
    Snowmelt said:

    if i go with taco shouldn't i just go with a delta T, especially if i use the outdoor reset that comes with the ultra.

    Why? ODR and constrained delta T operation may not get along.

    Here are some thoughts and explanation.

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Tinman
    Tinman Member Posts: 2,808
    Options
    Last winter alone on 6 Ultras, I replaced either the blocks under warranty or the entire boiler for those just out of warranty. I'd be much less concerned on the choice between Taco or Grundfos pumps. Both are rock solid.
    Steve Minnich
  • Snowmelt
    Snowmelt Member Posts: 1,415
    Options
    Ok hot rod, what if I don’t go with outdoor reset, and use the delta t pump
  • hot_rod
    hot_rod Member Posts: 22,142
    Options
    If the system meets these requirements, see below, the ∆T circulator will work. Personally I don't see any advantage to holding a constant ∆. If the delta wanders above or below the design a few degrees on low load, or high load conditions what's the harm?

    I've yet to find any heat emitter that must work at a specific ∆˙under all conditions? The ∆ in a system changes as a result of heat output.

    Probably more ∆T value in chilled water applications where tight ∆ is critical to prevent condensation.

    Opinions may vary :)

    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream