Weil Mclain CGA 6
Bladelock9
Member Posts: 2
in Gas Heating
Problem, boiler was working fine last season, shut it down for the summer and changed a few baseboard heaters. Now when I turn on the boiler and raise the temperature the boiler get running and in 10 minutes shuts down and only a few baseboards get hot not all of them. Then boiler starts for another 5 to 20 minutes and shutdown. It never reaches the temperature on the thermostat. What did I do wrong
0
Comments
-
-
What Tim said. You've got an air problem. Probably.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0 -
yup, sounds like air bound0
-
No they did not bleed the system after the install. Can I bleed the system?0