Indirect Tanks and proper Pumping
Pwall
Member Posts: 19
Quick easy pumping question.
I have a Utica H20 40 gal indirect water heater. It's currently being fed by a Taco 007 ECM pump from a Utica Trifire Boiler 4075. This circulator is dedicated to the DHW tank.
There are 2 other zones but they have their own circulator and the DHW has priority.
The documentation I can find on the tank indicates the ideal flow would be 14 gpm at 5.7 ft head.
Those flow requirements are a bit over what that pump is capable of. It's probably flowing around 12 gpm or maybe around 11 for that head.
Should the pump be ok even though it's a bit under powered or should I look at something more powerful even though at those performance specs it gets pretty pricey?
Or possibly parallel pipe 2 small cheaper 005 size pumps to split the gpm requirements?
I have a Utica H20 40 gal indirect water heater. It's currently being fed by a Taco 007 ECM pump from a Utica Trifire Boiler 4075. This circulator is dedicated to the DHW tank.
There are 2 other zones but they have their own circulator and the DHW has priority.
The documentation I can find on the tank indicates the ideal flow would be 14 gpm at 5.7 ft head.
Those flow requirements are a bit over what that pump is capable of. It's probably flowing around 12 gpm or maybe around 11 for that head.
Should the pump be ok even though it's a bit under powered or should I look at something more powerful even though at those performance specs it gets pretty pricey?
Or possibly parallel pipe 2 small cheaper 005 size pumps to split the gpm requirements?
0
Comments
-
The 007 will work just fine. In order to get the max capacity out of the indirect, the boiler would need to about 50% larger. Moving the water a little faster will have little or no impact on the performance of the system."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements