Insulating a radiant slab
mburg
When building a pole barn with radiant heat What is the recommended way to insulate the perimeter of a slab specifically at the locations of garage doors?
The edge condition is tricky. If you put it on the outside, you need to find a way to protect it from the weather and insects. On the inside, it forms a crack that some find undesirable. Here is a detail that works pretty well.At the garage door, it has to go on the outside, the 45 degree bevel at the top will help. You could make a metal slip plate at the transition.
Albert Einstein0 -
How high up should you go with the insulation at the garage doors? I would imagine you wouldn’t want to go all the way up to the top of concrete floor.0
You want to avoid the raw edge of the foam showing. They make a plastic H cap to go over 1/2" foam for isolation between slabs. After the pour you zip the top and put a bead of polyurethane caulk in the space. Not much R-value but some isolation for het transfer and movement.Bob "hot rod" Rohr
Living the hydronic dream0 -
We always put it inside the perimeter, 24" vertical and flush with the top of the concrete. The 2" raw edge will be buried within the wall cavity so it will never be seen, same with the sides of the poles. At the inside of the poles, it gets beveled up to 1/2" on top which again is covered by interior sheathing and acts as a barrier between the concrete and the pole in case of frost shifting. As for the door location, I haven't found anything better than a 45* bevel to a knife edge as of yet unless there is an apron outside. The local lumberyard here sells a 2" thick composite type plank with an R value of 7 that is similar to the material they use for joint control. It's ugly to look at and doesn't stay put unless there is an apron, but it does a good job IMO. Better R-7 at the surface than R-nothing0
It appears there isn’t a great option for insulating between interior slab and exterior slab at garage doors. On another note should I tape my insulation joints? I am putting down a vapor barrier under the foam board and taping that. Wasn’t sure if I should tape foam board too?0
I tape mine.0
SnapCap is the product I used, this company has the expansion joint trims.
https://www.wrmeadows.com/data/324.pdf
- 87.8K THE MAIN WALL
- 133 Chimneys & Flues