Hello. I'm planning on some changes to my heating system (hoping to save on heating costs this winter), and I want to see if what I'm planning will work (or, more to the point, what issues there may be in doing things this way). As of now, there are 2 zones on my ~3500 sq foot home, hot water / copper baseboard. During the winter / evenings, we really only need to heat the bedroom. I have a programmable thermostat downstairs to allow that, but there are 2 bedrooms upstairs on the one zone / loop, and a single feed / return feeding them. Would I be able to install zone valves upstairs, keeping the shared feed and return? I realize that reducing the zone size too far can lead to noise / erosion / etc, and that I may need to adjust the thermostat / hydrostat settings to avoid short cycling the boiler and maintain flue temperature, but is there any hard and fast reason not to do things this way? I don't mind work / fine tuning things, but if I can I'd really like to avoid running new lines from the basement to the second floor.
0
Comments
-
In answer to the hard and fast reason... not really. However. First, you may wind up with one very small zone (that one bedroom) and, unless you have a buffer tank, the boiler will short cycle. Second, unless you have a delta T pump on the zone you are splitting, you will be overpumping when just the one zone is open, leading to a low delta T and high return temperatures.
Third, and perhaps most important... you are really talking here about a form of setback, and setbacks usually (there are exceptions) don't save much energy...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements