radiant floor with aluminum plates
Snowmelt
Member Posts: 1,425
i have a question, the last bay at a job sight is only 10 inches are so. so i can only get one track in there would it be wise to put a track on the outside wall as close to the top as possible, to help prevent the cold air from coming in?
0
Comments
-
I would think you would want insulation to stop cold air from infiltrating. To me, cold air would extract heat from the tubing.
There was an error rendering this rich post.
0 -
-
-
The key is to get all the tubing that the design called for, installed. Don't skip a bay and shorten that loop.
If it is the outer most joist bay, the wall is above a portion of it, I'd just pack that one with insulation. Your highest delta T is that outer joist where ambient outside temperature is only 1-1/2 or 2" away from inside air temperature. Spray foam first to seal any air gap and pack a large fiberglass batt in there. Same detail for rim joist where the joist ends nail to the rim board, fill up that space with insulation.
Run 4 tubes in the last space if you need to use up the loop, two in plates two just fastened to the subfloous areu'h inBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements