Steamers eating checks....
Timco
Member Posts: 3,040
Both mine and the customer’s, lol.
I have 2 industrial checks on a 1.8 mil system, 2” feed. The double check setup lasted a year.
What’s next? Both ends? Triple?
I have 2 industrial checks on a 1.8 mil system, 2” feed. The double check setup lasted a year.
What’s next? Both ends? Triple?
Just a guy running some pipes.
0
Comments
-
-
I have a very large steam boiler. 1.8 mil. Has collection tank. Tank is below boiler in another room. The checks on the feeder from tank to boiler keep failing. I had 2 industrial check valves on it and it lasted a year before water is running back from boilers to tank. It’s eating check valves and the customer will be writing another check. I was on my phone.
Looking to upgrade the check placement or use to stop this one final time.
Thanks for any thoughts.Just a guy running some pipes.0 -
What pressure is this system running?
Are there any chemicals in the water?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Are the existing checks swing or lift type?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
You're somewhat over my pay grade, but I'll chip in with two cents anyway: can you switch to pilot controlled slow closing checks? I used to specify such things on big water pumps...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
They ship steam boilers here but no cool steam parts. I’ll have to order anything past standard checks. There’s cool how water stuff but no steam.Jamie Hall said:You're somewhat over my pay grade, but I'll chip in with two cents anyway: can you switch to pilot controlled slow closing checks? I used to specify such things on big water pumps...
Just a guy running some pipes.0 -
Try industrial lift-type checks. They should be less likely to slam shut.Timco said:All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I like the angle pattern swing checks. You have to use 2 per ASME code 1 at the pump and 1 at the boiler. Are they using a lot of MU water?
a better fix would be have a motorized valve (belimo or other) with an end switch (if you have multiple boilers). The boiler pump control opens the valves the end switch starts the pump.
Low end China valves are crap. You have to pay $$ to get something decent.0 -
I have 2 at the boiler and one on each pump at tank. The two at the boiler are angle swing industrial. They were $$.EBEBRATT-Ed said:I like the angle pattern swing checks. You have to use 2 per ASME code 1 at the pump and 1 at the boiler. Are they using a lot of MU water?
a better fix would be have a motorized valve (belimo or other) with an end switch (if you have multiple boilers). The boiler pump control opens the valves the end switch starts the pump.
Low end China valves are crap. You have to pay $$ to get something decent.
The big dog runs during winter, and now it’s an 800k just for DHW.Just a guy running some pipes.0 -
what is the failure, breaking. leaking, wearin the gate?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
If the metal is being eroded away, often it is excessive velocity and/ or aggressive fluid.
Cavitation is a very powerful force, it can erode away most any material in short order.
High temperature really accelerates corrosion also.
No harm is having the water tested at the device if possible. It could be a combination of events.
I doubt the brass quality of a brand name brand valve would be an issue, most everyone uses DZ brass alloy now.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
There’s a 2” BV above the 2) 1” lines from the duplex pumps. I had that off about 1/2 and it instantly stopped the banging. Better checks also helped. It’s double 2” at boiler horizontal and a 1” over each pump vertical. Pump checks were put in by maintenance guy and failed. Hinges flop. I’m doing all new industrial and speak to chemical guy. It’s real slimy water and low ph. System water very clear, some sludge in LWCOs and sight glass bases.Just a guy running some pipes.0
-
Maybe the checks are oversized? When a swing check gets oversized inadequate flow will cause the gate inside to float around mid position and chatter or bang. That will wear or destroy the valve quickly.
The Cv on a check is in the full open position and the valve needs that GPM to shove the gate open and out of harms way.
Check the Cv on the valve and compare to the actual flow rate passing through.
Often times a check can be several sizes smaller that the line it is connected to. If it is he style where the gate swings up and out of the flow path, for example, it will have a very high Cv.
Maybe a different style valve, as others mentioned would be a better fit?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
You mentioned banging. Any possibility of the feed water flashing into steam? Water through a high resistance valve. just guessing. Is the feed water really hot??0
-
The valves on the outlet of the pumps are control valves. their purpose to trottle the pump discharge. Restrict pump discharge and banging and check valve issue will go away.Gennady Tsakh
Absolute Mechanical Co. Inc.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements