Hoffman Bear Traps
the_donut
Member Posts: 374
Has anyone ever put a big mouth on the high side inlet to increase the venting of these traps?
Two pipe steam. I've got about 200' of 6" per main (2 branches total) and these traps seem to be the bottleneck. Headroom is a little tight along the piping and there is quite a bit of asbestos insulation I don't want to disturb.
Two pipe steam. I've got about 200' of 6" per main (2 branches total) and these traps seem to be the bottleneck. Headroom is a little tight along the piping and there is quite a bit of asbestos insulation I don't want to disturb.
0
Comments
-
Where are these traps? Are they crossover traps (ends of mains to dry returns?). If so you don't want venting there, but there would be no harm to piping any steam trap - such as a Big Mouth -- in parallel (that is, side by side) with the existing ones.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
What size and model is this Bear Trap? Assuming the branches are evenly split at 100 feet each, you have 20 cubic feet of air to vent from each branch. So the bigger the pipe size of the existing traps, the better.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
IIRC the traps are FT015H-3. They are placed at the end of the 2x 200' 6" mains. The are connected to a 1-1/2" verticle drop that elbows into a pitched downward return about 20' into the receiver of a bfp. The receiver is vented via 1-1/4 pipe.
System runs on pressure currently. I want to hook up indoor sensor to controller instead. Issue is system vents primarily through radiators and unevenly. I plan on slowing radiators down by installing orifice in shutoff valve, but I would like to increase venting on the steam mains as the traps vent slowly (0.950 cfm @ 3oz).
I was wondering if the FT015H-3 inlets are connected inside trap body. If so then I could simply plumb an elbow up out of top of trap and make an antler to vent instead of removing insulation and tapping (something I wouldnt want to do knowing the history of this building).0 -
They are connected inside, and so are the outlets. So you can actually install a high-capacity thermostatic trap- or a manifold with several such traps- as a bypass to the F&T, directing system air toward the condensate receiver vent.
We've used Nicholson high-capacity traps to do this, but the B&J Big Mouth crossover traps are much easier to get. These are available in 1/2" and 3/4" sizes, and IIRC the throughputs are the same.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
@Steamhead
Do you plumb inlet of bear trap -> crossover trap -> outlet of bear trap or inlet of bear trap -> crossover trap -> and tie in to line to receiver? Would their be any cons in just venting to atmosphere before the trap by plumbing a couple of big mouths in an antler connected to top of inlet?
I like the prospect of tying into vent line to keep vacuum without having to modify the big mouths.0 -
Either way will work. I prefer discharging the Big Mouths into the return since that will avoid the problem of water spillage in case the system floods. And it would also allow for vacuum operation, as you say.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Barnes & Jones will make you a crossover trap designed for normal crossover trap replacement. Same capacity, but the O ring is replaced with a brass seat. Needs to be ordered directly from factory.Peter Owens
SteamIQ0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements