Bad Steam Near Boiler Piping
Distance
Distance Member Posts: 6
Just bought a duplex with two steam boilers last fall. I read Dan's books and have been lurking here all winter. Had an issue last winter with the one below surging and banging pipes. I know it needs skimmed as well, but this is pretty bad piping yeah? No header, no hartford loop, odd equalizer setup, etc, etc.
I am going to repipe the boiler this summer and looking for your advice. Piping it how the manual has the header layout seems like it would be hard without moving the boiler (because they installed it so the right riser is directly below the steam main. I was thinking of taking both risers up into a header and then 90 (at the right side riser ) into to the equalizer in the back which will changed to a straight drop. After the 90, on the way to the equalizer, I will 45 up and go into the steam main. Would this be a problem? I'm not sure if 45ing into the main would cause issues, but can't think of how to pipe it without 45ing it because of how they installed the boiler with the right riser directly below the steam main. Any ideas or thoughts on this idea?
My Boiler:
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    This would be a great use for a drop header, using both outlet risers, and a proper equalizer. I don’t know that you have to go to the trouble of removing the ineffective connection between the outlet, and the wet return. Just make sure the header is one size bigger than the risers.—NBC
  • newagedawn
    newagedawn Member Posts: 586
    well now, there's an example of good piping principles, ah NOT
    "The bitter taste of a poor install lasts far longer than the JOY of the lowest price"
    GBart1Matthias
  • GBart
    GBart Member Posts: 746
    Fine example of a Hartford Slide
    1Matthias
    Steamhead Member Posts: 18,207
    That looks like a Utica PEG-112. The manual is here:
    http://www.uticaboilers.com/sites/default/files/240009937 REV D PEG IOM.pdf
    Consulting
  • GBart
    and your sight glass is awful dirty, download the manual for that boiler and follow the piping instructions, it's as simple as that, the manufacturers make these things called installation instructions in the hope that someone might read them, usually they are the first thing to get chucked to the side or tossed