Diagram for radiant
Snowmelt
Member Posts: 1,425
I want to install a traditional boiler, maybe install the taco fuel Mizor 3 zone, 1 radiant floor, 2 baseboard, would this be a good diagram to start with, I’m more concerned with boiler protection.
0
Comments
-
Personally, I would go with a smart mixing valve like the taco I-series for the zone mixers. They have outdoor reset and boiler protection built in. That would also eliminate the need for the boiler mixing valve."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
the expansion and circ need to be on the supply side
"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0 -
-
Thanks the only thing I’m thinking of adding would be a dirt mag0
-
If you use a Sep 4 it has a magnet included. Air, Dirt, Magnetic, and Hydraulic separation.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0