Is my "standby" Fuel Oil consumption high ???
Leonard
Member Posts: 903
Have hour meters on burner and circulator. Finally been warm lately so I can get a handle on standby losses, FHW circulator hasn't run for 3 days. So burner is only supplying standby losses and domestic HW. Tankless DHW coil in furnace water jacket
My hour meter on burner has been averaging 0.9 hour/24 hours. 1.1 GPH nossel, so 1.0 gal/24 hours. Does that sound high?
Only two ~ 10 minutes showers per day, and quick handwashing ( two 60 year olds). Old pre 1.1GPM shower heads, 40 psi water. Without old waterpik shower head attached to shower spout flow is ~ 3 GPM on cold water , less on hot (boiler has 5 GPM orfice) Cold water input is 42 deg F.
60 year old National Sunray IV , boiler # 5-19A/O/OP , rated 128k BTU/hr 1.6 gal/hr
Has original burner, National -US model NB2-K2, firing rate .85-2.0 gal/hr, nozzle = 1.10/ 80 deg/ B
Chimney is ~ 4 stories from cellar floor to top. No motorized damper for when burner is off, has barometric damper.
My hour meter on burner has been averaging 0.9 hour/24 hours. 1.1 GPH nossel, so 1.0 gal/24 hours. Does that sound high?
Only two ~ 10 minutes showers per day, and quick handwashing ( two 60 year olds). Old pre 1.1GPM shower heads, 40 psi water. Without old waterpik shower head attached to shower spout flow is ~ 3 GPM on cold water , less on hot (boiler has 5 GPM orfice) Cold water input is 42 deg F.
60 year old National Sunray IV , boiler # 5-19A/O/OP , rated 128k BTU/hr 1.6 gal/hr
Has original burner, National -US model NB2-K2, firing rate .85-2.0 gal/hr, nozzle = 1.10/ 80 deg/ B
Chimney is ~ 4 stories from cellar floor to top. No motorized damper for when burner is off, has barometric damper.
0
Comments
-
Does sound a bit high. Your showers are using a total of about 400 to 500 pounds of water, with a 60 degree temperature rise -- which works out to only 24,000 to 29,000 BTU. 1 gallon of oil is around 140K BTU... even if your boiler is only 50% efficient (which is quite possible at that age!) that's still about 70K BTU. Hard to say where the rest is going -- unless it is, as you surmise, standby losses.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'm assuming chimney is the dominant loss, no motorized damper0
-
-
-
at the very least get a outdoor reset control0
-
A gallon a day with domestic coil is about right. I bet less than 25% of the BTUs get the the DHW in the summer.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
System 2000, no standby loss, mine runs 2 10 min cycles in the summer for h/w, I burn about 1/4 gal a day from May through October0
-
Sounds right to me, I used to use 200 gallons easy over the summer on tankless. A new setup will pay for itself easy. You just have to buy it right and not pay some shmuck oodles of dollars to botch your install for you. That is much harder than it should be, that I can tell you. Try the find a pro link.0
-
I like using solar imdirects. Has a coil so the boiler males the hot water during the heating season, and an electric element so you can turn off the boiler completly during the summer. This does not work well with old boilers though, as most leak when they actually cool down.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!1
-
As I took a shower last night I measured shower flow for 1 minute with a plastic bucket...was 3 GPM. Immediately stuck my thermocouple in bucket, water was 101 deg F. February cold water is 42 degs so ~ 60 deg rise. And 88.5k BTU/hr heating rate, (tankless coil)
Assuming two 10 minutes showers /day that's ~ 29.5 kBTU /day.
You nailed it Jamie.
Not ready to change hardware yet, first want to see what I'm using, and learn some things first.
Turns out my OLD boiler pressure safty valve is leaking, so boiler may not be. Even though I heard it hissing from firebox when I ran out of oil couple years ago and boiler cooled to ~ 90 deg
Boiler is a nice quite 1800 rpm unit, unlike the new 3600 rpm ones.0 -
To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
-
This is where we get into what the actual efficiency of a tankless coil is.....its pathetically awful in the summer! Lots of standby loss, we affectionately call them chimney heaters!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
chimney heaters .... true enough. However I HATED running out of shower hot water in my 1-st apt. (electric hot water tank.)
That brings up another point, I did consider adding a motorized exhaust damper to limit chimney losses ( more for winter losses) . But since that might ultimately cool chimney I wonder if that would lead to more corrosive condensation in chimney and also cause reduced "draft" over fire problems. My chimney is ~ 9"x13" size red "tile" ~ 3 ft sections. ~ 4 stories from cellar floor to chimney top.0 -
I would just quietly note... that an often overlooked option, if one is burning oil anyway, is an oil fired hot water heater. Efficiency isn't that great -- 85% on the one in the building Cedric lives in -- but not that horrible either. If the current one lasts 20 years I'll be real happy. However... that same building can, on occasion, have as many as 20 guests at once, with five full baths... and never runs out of hot water (believe me, as the super I'd know right away!)Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I think a Bock direct fired oil water heater has a 65% real world efficiency. They will make copious amounts of hot water though. I grew up with a Bock in the basement. Lasted 24 years too. Replaced it with a used Bock I pulled out of a house that went propane. My parents are still using it.
I service a couple of kids summer camps. They both have like 10 showers all served by a single Bock.... but kids camp ain't the same as Jamie's place!Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
I have a Bock, 32 gallon, I get hot water and use for hydro-air heat in half my house. It is the standby loss that kills the efficiency on these things. Mine is about 15 years old. Water quality has a lot to do with how lone these things last.0
-
And maintenance. Most people never check/replace their sacrificial rods.Jon_blaney said:...Water quality has a lot to do with how lone these things last.
There was an error rendering this rich post.
0 -
Yeah the 6" vertical flue with a short turbulator at the top makes for a lot of standby loss.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements