Clogged Pigtail: 1; Big Mouth Air Vent: 0
JohnNY
Member Posts: 3,305
So, my pressuretrol was set for 1.5 PSI max.
But my pigtail was clogged, and so we went up to 4 PSI. This gauge picture was taken about a minute after I turned off the boiler:
Evidently the Big Mouth, though it's a loveable air vent, is unable to hold back some water the way some vents do:
But my pigtail was clogged, and so we went up to 4 PSI. This gauge picture was taken about a minute after I turned off the boiler:
Evidently the Big Mouth, though it's a loveable air vent, is unable to hold back some water the way some vents do:
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
0
Comments
-
Don’t feel so bad @JohnNY, despite what anyone says, you can bet the gorton # 2 would be a shower at those pressures too.0
-
Maybe if some dirt got caught in it. But this is why we don't spec Big Mouth vents on "B" dimensions.Danny Scully said:Don’t feel so bad @JohnNY, despite what anyone says, you can bet the gorton # 2 would be a shower at those pressures too.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1 -
Don't shoot the messenger. They're really should not be that much water in the system. The solution is not to install an air vent that traps the water in the system. The solution is to eliminate the water and its causes. Customer is almost better off having water spray out this way. It ensure that they will eliminate the underlying problem.0
-
Well, yes, @STEAM DOCTOR -- which underlying problem, in this case, was the clogged pigtail, which @JohnNY caught right away (no surprise there!). I'm with @Steamhead on this one.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Steamhead, are you saying we would be better off going with gorton's over big mouth's? My system works off of a vaporstat and cuts off at 14oz.0
-
i personally like a main vent that would let water spill out in basement in the event of mishap verse sending upstairs. I've seen 30k damage to hardwood floors caused by flooded systems that leaked upstairs.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.2 -
How about in a finished basement with no floor drain or sump pump? We see plenty of those...........All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
There is no such thing as 100% safe. However, there is much that can be done to increase one's margins.
On basement main vents, I'm going to have to agree with @Steamhead -- despite the much higher capacity of the Big Mouth, if there is a reasonable possibility that the pressure in the system may rise high enough to send water into the dry returns or mains where the vents are, I'd rather see vents with floats -- that is Gortons or big Hoffmans.
But -- it would be very good if water couldn't rise that high. Therefore, if you are not blessed with an operating vapour system control device (such as a Hoffman Differential Loop) which eliminates that problem (there are others which it doesn't eliminate) you really should have a second pressure control set low enough so that while water might get into the basement dry returns, it won't get any higher. Such as a pressuretrol set at say 1.5 psi. Which, as this thread points out rather well, should be on a different pigtail from the primary pressure control. If you are really paranoid, you can have a third manual reset control set at something clever like psi (12 feet)...
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
The output of that thing is threaded, right? Maybe you could put an elbow facing down, and leave a bucket under it.0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements