The boiler will not light off. I have air flow and spark but no fuel.
I can see the blue arc if the igniter through the view port and hear the relay click.
I do not smell natural gas from the boiler exhaust
There is good air flow from the exhaust
The gas supply pressure to the boiler is 10.5"H2O
I can hear the relay for the gas valve click and have 24VDC to the gas valve
Resistance across the gas valve solenoid is 185K OHMS
Both fuses are good on the control board.
I would think the resistance across the fuel valve solenoid should be 0 OHMS, can anyone verify that for me?
Thank you for your help,
Tom
I can see the blue arc if the igniter through the view port and hear the relay click.
I do not smell natural gas from the boiler exhaust
There is good air flow from the exhaust
The gas supply pressure to the boiler is 10.5"H2O
I can hear the relay for the gas valve click and have 24VDC to the gas valve
Resistance across the gas valve solenoid is 185K OHMS
Both fuses are good on the control board.
I would think the resistance across the fuel valve solenoid should be 0 OHMS, can anyone verify that for me?
Thank you for your help,
Tom
0
Comments
-
Check for amp draw on gas valve.0
-
Does inlet pressure drop during ignition?
Any codes? Series 2 or 3?
I've replaced many gas valves on the Ultra.
Use the CP# to see if its warranty.0 -
Gas pressure does not drop when the fuel relay kicks.
I do not have a meter to measure amp draw on the solenoid
0 -
The boiler is 14 years old so I think it is a series 10
-
fail to fire code
The fan is a little noisy and I don't have the ability to see the fan speed. I would think that the solenoid for the gas valve to open wouldn't kick if the speed permissive wasn't met.0 -
Bad or dirty gas valve0
-
call a pro, gas is not to be trifled with
0 -
Zero Ohms equates to no restriction to the flow of current creating a dead short circuit........overload blowing fuses or boards.
Your gas valve coil reading sounds as if it could be correct.
Sounds like you have a mechanical issue with the valve.
Remember..... if stuck shut......then somehow opens when called to do so.......can also become stuck open...........much worse problem than you have now!3 -
Natural gas or LP? 10.5" static is quite high for NG, but a little on the low side for LP. Don't think its related to your problem, but might be something to get corrected when you have the gas valve changed, which I'm pretty sure is your problem.0
-
-
Natural gas supply pressure requirements
1. Pressure required at gas valve inlet pressure port:
• Maximum: 13" w.c. with no flow (lockup) or with
boiler on
• Minimum: 5" w.c. with gas flowing (verify during boiler
startup, while boiler is at high fire)
Propane supply pressure requirements
1. Adjust propane supply regulator provided by gas
supplier for 13" w.c. maximum pressure.
2. Pressure required at gas valve inlet pressure port:
• Maximum: 13" w.c. with no flow (lockup) or with
boiler on
• Minimum: 4" w.c. with gas flowing (verify during boiler
startup, while boiler is at high fire)
from the manual0 -
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements