Hoffman Quick Valve Model 4 Not Closing
dkirkwood
Member Posts: 21
First, a big thanks to all who have responded to my questions over last months--I have trying to find where I am leaking steam, as the boiler is using about 1 gallon of make up water a week.
My system is a one pipe, wet return is completely exposed, not buried, not leaking. I have found several radiator service valves and vents that are leaking steam.
Today I checked the mains, which are only about 2 years old--Hoffman Quick Valve Model 4 --there are 2 of them--that was the valve that was there before I put in the new ones 2 years ago.
They are definitely not closing--or more accurately, a noticeable amount of steam is blowing out, well into the steam cycle, when all the house radiators are full of steam and hot--I am no pro, but I am assuming this is definitely not correct behavior.
Any thoughts on why they don't close? I am assuming dirt from the steam pipes is causing the problem--can these things be successfully cleaned and put back into service? If so, how do I clean them--just use vinegar soak as recommended for radiator vents?
Thanks for the help
My system is a one pipe, wet return is completely exposed, not buried, not leaking. I have found several radiator service valves and vents that are leaking steam.
Today I checked the mains, which are only about 2 years old--Hoffman Quick Valve Model 4 --there are 2 of them--that was the valve that was there before I put in the new ones 2 years ago.
They are definitely not closing--or more accurately, a noticeable amount of steam is blowing out, well into the steam cycle, when all the house radiators are full of steam and hot--I am no pro, but I am assuming this is definitely not correct behavior.
Any thoughts on why they don't close? I am assuming dirt from the steam pipes is causing the problem--can these things be successfully cleaned and put back into service? If so, how do I clean them--just use vinegar soak as recommended for radiator vents?
Thanks for the help
0
Comments
-
Vinegar soak may work. They are built very like radiator vents.
However. May I ask what your maximum pressure is? No vent likes pressure much...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Also, most times we encounter these vents, they're too small. How long are your steam mains, and what pipe size?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
the pressure is between 1 and 1.5 psi
As to second question: it is 2" pipe for the 2 mains--both are 38 feet long--do you think there is a better choice than the Hoffman 4 for this pipe size/length and operating pressure?0 -
Sure is. If you have the headroom, put a Gorton #2 on each one. These vents are 6-1/2" tall, including the part that threads into the pipe, so measure before you buy them. But they will make those H-4 vents look like toys.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks for advice--I have to get into a crawl space to measure so I will tomorrow--one question...if there is a joist directly above the valve--would it be permissible to add an elbow to the current riser nipple, the use a small nipple with another elbow to position the valve so it's height could be accommodated in space between joists?0
-
That's what I'd do. Just make sure the horizontal portion pitches back toward the steam main, so it doesn't hold water.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements