Hoffman Quick Valve Model 4 Not Closing

dkirkwood
dkirkwood Member Posts: 21
edited April 2018 in Strictly Steam
First, a big thanks to all who have responded to my questions over last months--I have trying to find where I am leaking steam, as the boiler is using about 1 gallon of make up water a week.

My system is a one pipe, wet return is completely exposed, not buried, not leaking. I have found several radiator service valves and vents that are leaking steam.

Today I checked the mains, which are only about 2 years old--Hoffman Quick Valve Model 4 --there are 2 of them--that was the valve that was there before I put in the new ones 2 years ago.

They are definitely not closing--or more accurately, a noticeable amount of steam is blowing out, well into the steam cycle, when all the house radiators are full of steam and hot--I am no pro, but I am assuming this is definitely not correct behavior.

Any thoughts on why they don't close? I am assuming dirt from the steam pipes is causing the problem--can these things be successfully cleaned and put back into service? If so, how do I clean them--just use vinegar soak as recommended for radiator vents?

Thanks for the help

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 23,986
    Vinegar soak may work. They are built very like radiator vents.

    However. May I ask what your maximum pressure is? No vent likes pressure much...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Steamhead
    Steamhead Member Posts: 17,177
    Also, most times we encounter these vents, they're too small. How long are your steam mains, and what pipe size?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • dkirkwood
    dkirkwood Member Posts: 21
    the pressure is between 1 and 1.5 psi

    As to second question: it is 2" pipe for the 2 mains--both are 38 feet long--do you think there is a better choice than the Hoffman 4 for this pipe size/length and operating pressure?
  • Steamhead
    Steamhead Member Posts: 17,177
    Sure is. If you have the headroom, put a Gorton #2 on each one. These vents are 6-1/2" tall, including the part that threads into the pipe, so measure before you buy them. But they will make those H-4 vents look like toys.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • dkirkwood
    dkirkwood Member Posts: 21
    Thanks for advice--I have to get into a crawl space to measure so I will tomorrow--one question...if there is a joist directly above the valve--would it be permissible to add an elbow to the current riser nipple, the use a small nipple with another elbow to position the valve so it's height could be accommodated in space between joists?
  • Steamhead
    Steamhead Member Posts: 17,177
    That's what I'd do. Just make sure the horizontal portion pitches back toward the steam main, so it doesn't hold water.