Rebuilding Thermostatic Traps
josephc
Member Posts: 39
We recently purchased a home which has a two pipe steam system. I am learning about the system and have the lost art of steam heating and the we got steam books. The boiler was replaced with a weil mclain eg-50 prior to our owning the home and consists of four radiators. Not sure what boiler was there before but as I read I am learning more of what the system may have been originally.
I am seeing a number of issues with the system that I may be bringing up in future posts but for now I have a question regarding refurbishment of thermostatic traps.
The ½ inch radiator traps are three MILVACO H100 and one Barnes&Jones #122. Has anyone here rebuilt these traps before and if so should I go with the cartridge style kit or something else and of these three manufacturers – Barnes&Jones, MEPCO, TURNSTALL – is one any better for these model traps? Am I able to keep the existing covers? Anything else to be aware of when doing this work?
Thank you
Joe
Thank you
Joe
Barnes & Jones will make the repair kits for all those. The cage units are the same for all models you are asking about so performance will be identical. I'm obviously partial to B&J since I used to work there. They would also be making the cage units for Mepco.
Part for 122A is 1721 uses existing cover
Part for H100 is 3510 uses existing coverPeter Owens
SteamIQ0 -
If I am correct Peter, don’t the Barnes and jones replacements move more air during venting than the originals? I know it’s true of the hoffman 17c.0
That sentence does not compute...josephc said:The boiler is (sic) a Weil Mclain eg-50 and consists of four radiators.
New England SteamWorks
newenglandsteamworks.com2 -
@New England SteamWorks Agreed, that is a lot of boiler for 4 radiators.... unless they are somewhere around 110 EDR each....
Over sized much?0 -
It depends. On traps where the seat is removed, yes there will be an increase in venting. On traps with an integral seat the new cage unit has to fit down in the seat so venting will not be as high. Either way a cage unit reacts much faster than the bellows present in older traps which has efficiency gains.the_donut said:If I am correct Peter, don’t the Barnes and jones replacements move more air during venting than the originals? I know it’s true of the hoffman 17c.
Peter Owens
SteamIQ0 -
A Barnes and Jones rep emailed me that the 2164 with 2164C cover is more commonly used. I don't know if its because it is more readily available over the 3510 or if people have found it more difficult to use the existing milvaco cover.0
with regards to boiler size; we purchased home in 2015 and the boiler had been replaced by previous owners in 2011. There is evidence of at least two removed radiators from house.delta T said:@New England SteamWorks Agreed, that is a lot of boiler for 4 radiators.... unless they are somewhere around 110 EDR each....
Over sized much?
The EDR of the 4 radiators adds to 288. The eg-50 is 454 sq ft of steam. We are having an addition put on home which will add another radiator.0 -
Go with that then. Not sure who the rep is but sounds like they know what they are talking about. I honestly have no personal info about which is the better fit, it lists both options in the guide.josephc said:A Barnes and Jones rep emailed me that the 2164 with 2164C cover is more commonly used. I don't know if its because it is more readily available over the 3510 or if people have found it more difficult to use the existing milvaco cover.
Peter Owens
SteamIQ0
- 114 Geothermal