Taco SR 501 wont turn on boiler
parkingnotice
Member Posts: 16
This is a radiant floor system. Have new Thermolec TMB boiler replacing Hydro Shark boiler. The HS was switched from a Taco SR501 which started the pumps, which ran the water through a flow meter, which kicked on the boiler. There were no TT connections inside the boiler itself. The Thermolec works differently and has its own pump relay and control board with C and W1 contacts inside the boiler. C and W1 on the boiler are wired to 6NO and 5 on the Taco as per the Taco and the Thermolec diagrams. I have 120v into the Taco. I have 24v at the TT terminals in the Taco. The Taco is on (green light), I call for heat (red light) and then nothing. I thought the Taco, when TT calls for heat, is supposed to switch 6NO and 5 and send signal to boiler. I am getting 0 volts between 6NO and 5 all the time, Taco on or Taco off.
What am I missing? Am I supposed to be getting any reading between 6NO and 5? Or do I need to jump 24v to 5?
What am I missing? Am I supposed to be getting any reading between 6NO and 5? Or do I need to jump 24v to 5?
0
Comments
-
Don't jump 24v to 5.
What do you have on H and 3?
Why can't you just wire the thermostat to C & W1? Why do you need the relay?There was an error rendering this rich post.
0 -
My Thermostat is a Tekmar smart thermostat. It needs its own 24v supply. As per the Thermolec instructions I have to provide my TStat with its own power and use an isolation relay to switch the boiler.0
-
-
Ok. Thanks. I did try to jump 6NO and 5 and nothing happened. I will check the boiler when I get home.0
-
So your tstat is wired to the isolation relay coil and the TT contacts of the Taco control go through the relay contacts.0
-
Make sure boiler is in the Electric only position.0
-
Yes. My Tstat is wired to the TT terminals of the Taco plus the Com. It is a Tekmar smart Tstat. Smarter than me.
The 6NO and 5 then go out to boiler C and W1.
I'm not sure what you mean by "electric only position" except I think you are referring to the Thermolec boilers that are dual-fuel. This one is only electric. Is there still a switch? I'll look for that when I get home. There wasn't anything about that in the manual.0 -
If Jumping the electric boiler does not start it, I would start looking at the safety's. A flow switch or high limit...."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
I just found a note in the troubleshooting section. This wasn't in the manual at all. I found the troubleshooting pages in the brochure, but not the installation manual. Go figure. I do not have a load management control. I'm going to try and jumper the S1 and S2 when I get home.
0 -
Ok guys....S1 and S2 jumpered. Nothing. Ran through the testing sequence. I have no power on the 24v side of the transformer. So that's that. Brand new boiler. Contacted the manufacturer.0
-
-
-
Hilarious. Yes, of course. 240v on 60amp double pole breaker.
It was in fact the transformer. Dead on arrival. You’d think it got tested before it left the factory. Cest la vie.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements