Triangle Tube combustion vent pipe failures
smklin
Member Posts: 69
Does anyone have any issues with their triangle tube boilers combustion vent pipe splitting open and cracking
0
Comments
-
Mine is fine. I have replace one and I believe it was leaking at the bottom. That pipe was metal and the replacement was plastic. Are you having multiple failures?0
-
yes I have a total of 11 boilers and the hotter the working temp the worse it gets all of them will need to be replaced within a year0
-
PVC or CPVC pipe?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Your talking about the vent pipe inside the boiler correct?0
-
Which model? LP or Nat gas?0
-
What sizes? Concentric vent?0
-
the boilers I have are solo 250 and solo 175
no its not concentric vent the vent are about 5 feet till they terminate the buildings
its natural gas
the pipe that's cracking is the flue gas pipe inside the boiler
and I believe its a polypropylene pipe
https://www.supplyhouse.com/Triangle-Tube-PTRKIT116-Vent-Pipe-for-Solo-175-250-Trimax-Boilers-only0 -
This product is only compatible with boilers which have a Trimax Control.
Vent Pipe - polypropylene (for Solo 175-250 Boilers)
NOTE: Please do not call the manufacturer, Triangle Tube, with questions about this product. If you have questions (technical or otherwise), please call customer service at 1-888-757-4774 and a customer service representative will be happy to assist you.
Don't get me wrong I buy from Supply House but this tells me that you should be calling TT and talking to them. If there is a real problem with their stuff they will fix it.0 -
That's disconcerting... especially where we have been told/ fed that pvc is not good for venting boilers.
There are a lot of boilers/ mfg that use PP for the first leg going out of the combustion chamber.
What are you seeing for flue/ stack temps?
Got any pix?
0 -
I am dealing with triangle tube and it seams they are working with me .I am just wondering if this is a common problem.as far as supply house I don't buy from them .Was just a link to clarify what I was referring to.0
-
yes I have pic how do I post them0
-
On the leave a comment section there is an icon above where you type.... 3rd from the right0
-
The older TT's has stainless vents. They switched to poly when they introduced the Trimax model. If I remember correctly they claimed that they had had issues with something corrosive leaching from the PVC vent piping in the US market.
Keep us posted on this one."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
-
Silly (loaded) question: Is PVC allowed as venting in other parts of the world?Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
Still like to see a picture.....0
-
0 -
Wow, that's for sure a failure. Not sure what caused it, but it is breached...
To the other person who asked where else PVC is allowed, anywhere that they accept the manufacturers installation instructions, including Canada. The PVC manufacturers can make any claims they want about incompatibility, but the bottom line is, it's the boiler manufacturers who carry the liability, and they have done their research and have approved it for installation with their equipment.
I've never seen PVC fail like that.
METhere was an error rendering this rich post.
-1 -
I talked to triangle tube and they said they suspect that it comes from over firing I went and checked the combustion on all the boilers that failed like that and not one was the oxygen level over what the book said as far as the high limit .The high and low fire was not within + or - .2 but was not that far out of range ??????
0 -
Hmmm, that looks a lot like the W-M 97+/ECO inside. That same PP base and pipe too.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0
-
What did you do to repair it?
0 -
Over firing, BS, Then their flue sensor or other safeties should have shut down the boiler.
My personal feelings on their boilers is that they do not have good safeties implemented with their boiler operation. Have seen a few dangerous issues with the boiler over the past 14 or so years.
But I'm just a heating guy, no engineer here.
D
2 -
Nothing yet I am waiting for my supplier to get me the parts .These boilers are less than 6 years old .And it seams that the hotter the design temperature the worse it gets. They drill a whole in the flue pipe and install the flue sensor there it seams they start to crack there .On the new flue pipes they install some bushing type deal there to put the flue sensor in there.0
-
something else I noticed that the boiler will not keep its combustion analysis if you go and fine tune it to triangle tubes spec (have called in to there tech line and set the boiler to there liking ) it will not keep the combustion for let say a few months0
-
Years ago I worked with a guy we called "too tight Charlie" If a pipe needed a 1 3/8" hole, he would shove it into a 1". If a cooktop instruction said to make the opening 30 1/4", he would cram it into a 30" opening and wonder why the counter top cracked when the stove heated up. I haven't seen Charlie in years, I wonder if he went to work for Triangle Tube.
How much are your combustion numbers wandering around? The difference in temperature of the combustion air will effect the numbers quite a bit"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
And atmospheric pressure, and humidity, and solids in suspension (sheet rock dust) and, and, and,.Zman said:Years ago I worked with a guy we called "too tight Charlie" If a pipe needed a 1 3/8" hole, he would shove it into a 1". If a cooktop instruction said to make the opening 30 1/4", he would cram it into a 30" opening and wonder why the counter top cracked when the stove heated up. I haven't seen Charlie in years, I wonder if he went to work for Triangle Tube.
How much are your combustion numbers wandering around? The difference in temperature of the combustion air will effect the numbers quite a bit
In reality, the combustion analysis is only valid for THAT second in time, under THOSE operating conditions. Kind of like a stopped clock being correct 2 times per day...
But NOT doing an analysis is more dangerous than doing one and having those conditions change in the field. DO THE ANALYSIS.
ME
There was an error rendering this rich post.
1 -
That looks more like Polypropylene pipe. Is it?
Rick0 -
It would be good to clock meter in high and low fire, would be interesting to see if overfired. Also with water temp all the way up to max, in high fire, what is your flue temp. All of the above would be good to know. Sorry to see this, I have quite a few TTs out there. Other possibility is if there is a hole in the burner but I would think you would pickup on combustion readings.
Tim0 -
it does look like PP, not PVC?
PP is rated to 235F. When boilers get dirty flue temperature goes up. But sensors should protect against excessive temperatureBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I would say that the low fire was lower by average -.5 tents one was quit a bit more there were some of the boilers that were within + or - .2 tentswich is what tt wants they were all within range of what the book says as far as max oxygen level even the ones that were + or - .2 tents cracked .These boilers do high temp baseboard 160 degrees and domestic hot water were the boiler side of the domestic water is set at 160 degree .0
-
on another note these boilers never get up to 235 degrees flue temp they never go to 1800
-
Is the outdoor reset hooked up ?
There was an error rendering this rich post.
0 -
yes its hooked up the boilers have a max temp of 160 degree + or - a few0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements