Commercial boilers
SlamDunk
Member Posts: 1,684
We have several hps boilers and i noticed all flue dampers are 100% open. Is there a reason? The start up techs never looked at them. I was wondering if we are losing energy doing this.
0
Comments
-
@slamdunk, I am assuming that "hps boilers" means high pressure steam.
In any event, any boiler that has a damper in the flue the damper must be locked in the open position or if it's a motorized damper it must be driven open and proven open electrically before the burner can fire. If a damper is partially closed to restrict excessive draft at the boiler then it must be locked in position after combustion testing.
Something used widely in the past but not used as often now is "sequence draft control". These controls were usually made by "Cleveland Controls" or "Preferred Utilities" and used a damper actuator and controller to close the damper on the off cycle. Open it when the burner fired and operate automatically "float" to control the draft as the burner modulated from low to high fire. Not seen much any more.0 -
yes. high pressure steam.
Thanks! they are locked 100% open. I was wondering why they were installed but not used.0 -
Maybe to avoid a service call later when the dampers fail closed.0
-
0
-
forced draft. pipe straight to roof about 36’. burner has blower0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 59 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 374 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements