Water in pigtail
Matthias
Member Posts: 38
Hi everyone - I am curious if anyone has had any problems with water going into the pigtail on a Crown boiler. We installed this boiler in 2007 and installed a new block the summer 2017. Over the last 2 months, every 2 weeks or so, we get a call from the customer with no heat. Everytime we find water in the pigtail. Has anyone dealt with a problem like this before? Thanks for you help.
0
Comments
-
That water is actually supposed to be there,
and in fact, you should "prime" the pigtail after cleaning or checking it.
this is one time I am going to suggest raising ever so slightly the pressure setting on the P trol.
You might have it dialed down so far that when the water / condensate forms in the loop it offers just enough resistance to stop the trol from seeing boiler pressure.
dial it UP a 1/4 turn, or 1/2 turn, and watch a cople cycles.
that should do you.
Post a picture also, maybe we'll see something else.known to beat dead horses0 -
@Matthias
just think about this.
Steam is not supposed to reach a pressure control or a pressure gage. Some pressure gages will say "has internal syphon" on them. For a short period of time it will not hurt it.
When steam enters a pigtail loop it will get cooled because the room air surrounding the pigtail is cooler than the steam so it condenses into water........so you get water in the pigtail.
The water is supposed to be in the pigtail.....that's what protects the pressure gage or control from touching steam0 -
@Matthias: It may be the pigtail is clogged or rusted shut. Is the pigtail in question brass or steel? If it is steel, it should be replaced anyway, clogged or no.All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
a pic of the near boiler piping would be good"The bitter taste of a poor install lasts far longer than the JOY of the lowest price"0
-
@Gordo, I believe the pigtail is brass and I think we changed it when we changed the block. @EBEBRATT-Ed, thank for explaining that and yes that makes a lot of sense. @neilc and @newagedawn, we'll be going back next week to check the system and I will have our guys take some pictures. Thanks for everyone's help. Stay tuned!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements