Hi guys, I'm a newbie to the forum. I have an appt with a contractor to install a new Weil Mclain EG-30 boiler installed. The boiler being replaced is the identical boiler. My concerns lie with the way the original boiler is piped. I have included pics of what I'm working with. From my research I have a counterflow system because there are no wet returns at the end of the mains. I did have some water hammering with the original system. I also do not have a Hartford loop but I've read it's not extremely important with a dry return system (counterflow). Can anyone tell me whether or not the near boiler piping is designed okay?
0
Comments
-
From everything I've seen here, that tee should be split into 2 different mains off the header0
-
-
1. Was the connected radiator EDR calculated? Boiler needs to be sized to the connected radiation.
2. There is no header. You need a header, at least 24" above the boiler water line to allow water droplets to fall out of the steam before it enters the mains.
3. I don't see an equalizer on this system. You need an equalizer, at the end of the header. Configuration on the Header should be: Boiler riser, 2nd Boiler riser (if both are used), Main, 2nd main, equalizer at end of Header.
4. Those two mains should be split off of the Bull Tee and each drop into the new Header
5. Both Mains should have its own drip down to the floor.
6. You and especially your installer must read and understand the Manufacturer's I&O manual. That provides the minimum piping configuration and sizing.
-1 -
The_donut, there are 2 cents, one at each end of each right and left main pipe. The only condensate return is the piping near the boiler, it shares the same pipe as the main steam pipes. Leon82, the riser tees off into 2 main steam pipes. One feeds the front of the house, the other feeds the rear.0
-
Thank you free, all that seems to make sense.0
-
-
The_donut, I'm sorry, i have no clue. I'm an amateur/just a homeowner. I believe the diameter if the mains are 4". It's a 2 family house but this heating system is only for the 1st floor apartment. I didn't check to see if I have end of riser vents but I don't remember seeing any. It looks to be the most basic kind of system.0
-
From what I can see, they are probably 2" or maybe 2.5" mains and if this unit only feeds radiators on the first floor, there are no risers to worry about. Once the new boiler is installed, have the installer check and maybe replace the radiator vents, depending on their condition. I'm guessing you probably only have 4, maybe 5 radiators.-1
-
Fred, should I still have a header pipe installed? According to the weil mclain manual I need a 2" header pipe feeding into the top.of the main supply pipes if installed on a counterflow system. The manual states the riser should also be on the same side as the controls, which my current configuration is not. I have included screenshots of the weil-mclain manual I am referring to. Thank you very very much for your help/input.0
-
If it's counter flow with two main branches, it should be piped like this for best performance:
Certainly do not allow him to pipe the same as the current, that is wrong.
New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com2 -
-
If it means cancelling the appointment, or even eating a couple hundred bucks it's worth to ensure a properly sized boiler. You gotta live with it for years. This is a once in half a century opportunity to size it properly.MilanD said:And to stress it one more time: measure the connected radiator EDR to make sure boiler is sized to the connected load and not to the old boiler.
That being said the EG-30 looks like about the smallest boiler in that line. Less than 50mbtu.
https://www.weil-mclain.com/sites/default/files/field-file/WM1802_BRO_036 EG Web.pdf
0 -
@esco105 , yes, follow the diagram that @New England SteamWorks provided, above. There is:
- Both risers out of the boiler in use (ideal but that is a small boiler and minimum requirement is probably one riser)
- A header
- Both mains drop into the header
- Both mains have a drip
- Both drips drop to the floor
- There is a Hartford loop
- there is an equalizer
- per my original post, pipe configuration into the header is:
- boiler riser
- boiler riser
- riser to main
- riser to main
- equalizer at end of header, after the boiler risers and risers to mains
- a little pitch in the header, towards the equalizer so that water can run into the equalizer
- The diagram New England Steamworks provided uses a "drop Header (risers out of the boiler go up, then elbow back down into the Header. That makes for much drier Steam although the "minimum" requirement does not require a drop header, it is well worth the cost of a couple extra elbows.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements