Weird error code on Munchkin boiler - what does it mean?
ccarter2
Member Posts: 3
Hello all ~
Can someone help me? My Munchkin boiler is currently showing a weird error code on the control panel and it is not listed in the owner's manual troubleshooting descriptions. It looks like it reads: H.8.8. I can't find any reference to what it might mean. I tried pressing the 'reset' button, but nothing happens. Any of you experts out there have a clue??
I took a picture of it .... will try to post.
Thanks so much,
C. Carter
Can someone help me? My Munchkin boiler is currently showing a weird error code on the control panel and it is not listed in the owner's manual troubleshooting descriptions. It looks like it reads: H.8.8. I can't find any reference to what it might mean. I tried pressing the 'reset' button, but nothing happens. Any of you experts out there have a clue??
I took a picture of it .... will try to post.
Thanks so much,
C. Carter
0
Comments
-
New one on me. I would call HTP at 1-800-323-9651 and talk to technical. I think that it might be a bad display board trying to display 8.8.8. and missing some of the bars on the first 8.
You can check the cable and make sure it is seated on both ends. Remove the power to the display board and then the power to the boiler and see if it resets.
I always connect these new fangled mod/cons thru a computer grade surge protector. Lightning can strike 1/4 mile away and do havoc on a control board. I've seen it happen.2 -
Thank you very much, Homer, I will call that number. You may be right about missing bars on the '8'....I wondered that, too. I dare not fiddle with this unit myself (just a gal without such tech knowledge) but I was anxious that something dire might occur. And I do think it's extremely odd that I can't find any reference to that number sequence in the manual OR on Google.
Thanks again.0 -
-
Thanks for your reply, Mark.
At the moment, I am concerned about following the power on/off suggestion because although the error code is still on, the boiler appears to be running fine & the house/water is being heated, etc.
Could you possibly explain your thinking about the power-off? Also, have you heard of this particular code before?
Thanks again.0 -
The reason you don't see a fault code like you have is because it isn't a fault code. It's a failure in either the display board, ribbon cable, or controller. I suspect the controller is ok as you have heat from, what appears to be a normally functioning boiler.
Unplug the ribbon cable from the controller and re-plug it back in. You can remove the 4 screws from the display board and remove the ribbon cable plug from the board and re-plug it back. Do this with the power to the boiler turned off.
My bet is that it is a bad display board as all the leds are lighted up.
You can buy a new display board from http://jupiterheating.com/ and order one based upon the controller on your boiler. Different controllers require different display boards and ribbon cables.0 -
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements