Oil Boiler cycling on and off - short cycling?

jjohnson191jjohnson191 Posts: 1Member
Hello:

I feel kinda stupid asking, but is the operation of the Weil-McLain boiler that is described below and shown in the linked video normal? Is this “short cycling”?

Aside from the general concept behind their operation, I don't know a great deal about boilers but the motor was changed yesterday and I am wondering if the constant on/off cycling is what caused the old motor to fail (and I'm afraid it could burn out the new one).

Some background: It is a Weil-McLain boiler for a baseboard heating system that heats two zones—upstairs and downstairs (the hot water is on a separate propane system). I noticed a few weeks ago the boiler seemed like it was cycling on and off too often. Then, a few days ago, the boiler stopped working altogether with Red Light on. I did two Resets about 10 minutes apart using the red button but it wouldn't start. So I called a Tech and he said motor was dead and replaced it. But it still seems to me like it's cycling on and off too often.

In the video, the boiler is running when I started recording, then stops, starts, stops and starts again, but multiply this by 50 or so times since it does it throughout the day whenever the t-stat is calling for heat. Sometimes the boiler will run for an extended amount of time without any issue and it will bring the house up to temp. The cycling does seem worse in the morning when the house is cold.



A couple other pieces of info: a new expansion tank was installed in Dec 2017. Also (and this is just annoying but maybe it's related) the downstairs thermostat is way off in terms of the actual temperature in the room. The stat will read 61 when it’s actually 67 or 68 in the room.

I haven't tested this, but I feel like the cycling issue occurs only when the downstairs t-stat is calling for heat. Is it possible the short cycling (if that's even what is happening here) is a result of a defective t-stat calling for heat too often/too little/too sporadically?

I guess I could test this by basically turning the downstairs zone t-stat way down and turn the upstairs t--stat up and see if when the upstairs calls for heat the cycling issue does or does not occur. Maybe I'll try and test this sometime in the next day or two but would like to know, firstly, if what is happening in the video is actually abnormal.

Any thoughts would be much appreciated and please feel free to ask for any clarification since I don’t know what the heck I’m talking about.

Best, James

Comments

  • the_donutthe_donut Posts: 369Member
    You could try replacing the downstairs thermostat, sounds like it is time anyway. Did he replace circulator with a larger size?

    I am assuming there are some valves. It could be that downstairs loop has a wiring issue after install. Loose connection somewhere.
  • Jamie HallJamie Hall Posts: 8,534Member
    To answer the basic question -- no, it's not normal and it shouldn't be doing that. The idea of trying one loop at a time is excellent -- do it. If that isolates the problem to one loop, then step by step troubleshooting of that loop is in order.

    If it doesn't isolate it to one loop or the other, then step by step troubleshooting of the actual burner controls is in order -- things like zone end switches or relays, or more likely the aquastat.
    Jamie



    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.



    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • EBEBRATT-EdEBEBRATT-Ed Posts: 4,181Member
    You just need a technician with a brain. No. it shouldn't be short cycling.

    There are a multitude of things that could cause this.

    controls not set properly
    baseboard air bound
    defective thermostat
    grossly oversized boiler
    circulator air bound
  • STEVEusaPASTEVEusaPA Posts: 2,148Member
    I agree with Ed (about everything except...well you know Ed ;) ).
    Looks like that temperature gauge is showing that maybe your circulator isn't running or that you are air bound (you mentioned exp tank replacement).
    Watching, isolating, testing, measuring should find the problem in short time. If it was rapid fire on-off-on-off, I'd suspect a wiring or control issue.
    Also looks like you had or have a draft problem or dirty boiler with the door around the inspection port looking like it took a tremendous amount of heat. Maybe the chamber door panel is damaged.