    Is my condensate pump louder because of the weather?
  • Youssef1971
    Youssef1971 Member Posts: 1
    Options
    Our feed pumps continuously cavitated , can we know the reasons ?
  • Jamie Hall
    Jamie Hall Member Posts: 23,338
    Options
    The overall reason is low "net positive suction head". Which, I realise, isn't a bit helpful unless you know what it means.

    Which is that there must be a minimum absolute pressure at the inlet to the pump, which is dependent on the pump construction and -- assuming water -- the water temperature. That's absolute pressure, not gauge pressure.

    Why might this be the case? One reason is excessive restriction in the inlet piping. One reason is too much suction lift. A very common reason in heating applications is inadequate static head (the level in the tank vs. the elevation of the pump) combined with warm or hot water.

    There are secondary problems, too -- such as an elbow too close (less than 10 pipe diameters) from the intake, or a valve which isn't full port within the same distance.

    Good general practice would be to ensure that the pipe is straight and unobstructed for at least 10 diameters before the pump and there is at least two feet of water over the inlet at all times, even for cold water -- and more for hot water.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • dopey27177
    dopey27177 Member Posts: 887
    Options
    If your condensate temperatures are above 160 degrees and if the pump is a rotating at 3200 rpm and above steam is forming in the eye of the impeller therefore the pump can not pump water.

    The steam caused the prime in the pump to be lost.

    I assume you have a steam system with steam traps, if so look for defective steam traps that are passing steam, If this is a system that supplies heat for a building only, lower the steam pressure to no more than 2 PSIG.

    Jake