Hartford Loop BANG BANG
EBEBRATT-Ed
Member Posts: 16,098
Saw a job today with a boiler feed tank and pumps. The installer did a nice job, it's a school and the boiler is about 15 years old. The custodian complained that when the feed pump is on the boiler hammers, has always done it since day 1 nobody can fix it. The feed pump discharge is piped into the Hartford loop so it's probably shooting some water into the header when the pump runs.
We throttled the pump discharge and it was much better and had no problem keeping up feed water wise.
If you have a feed pump DON'T pipe it into a Hartford loop. Just pump it into the boiler return. The Hartford Loop connection is for gravity feed only. You can't back water out of a boiler with check valves on the feed pumps. Yes of course you still need the equalizer, just don't pump into the equalizer.
My 2cents
We throttled the pump discharge and it was much better and had no problem keeping up feed water wise.
If you have a feed pump DON'T pipe it into a Hartford loop. Just pump it into the boiler return. The Hartford Loop connection is for gravity feed only. You can't back water out of a boiler with check valves on the feed pumps. Yes of course you still need the equalizer, just don't pump into the equalizer.
My 2cents
1
Comments
-
I've always wondered about this. When I started in the boiler trade 11 years ago everyone always told me that the Hartford Loop was 100% necessary. After reading some of Dan's and Ray's material I have found that is not true and it makes sense.
But I am wondering if the inspector would agree with that. Every new boiler I see today that has a feedwater tank still has a Hartford Loop with the feedwater piped into it. I will have to do some research and see if that would pass around here in Washington DC. I completely agree with you and it would be a much better option.Never stop learning.0 -
Absolutely. It's pumping in to resistence & weight of water. Mad dog0
-
And it is often shown that way in various install manuals. But we are assuming that the inspectors know what a Hartford loop is for.0
-
-
Absolutely right, Ed. Well done. Thanks for sharing here.Retired and loving it.0
-
Mad Dog, good idea. I will ask Dan Foley. Thank you!Never stop learning.0
-
After checking, apparently inspectors in DC still want a pumped return piped into the Hartford Loop.Never stop learning.0
-
They need to be educated.Retired and loving it.0
-
-
Send them here.Retired and loving it.0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 892 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements