Anyone installing the Watts Onix radiant tubing system.
Customer looking at using this tubing for a radiant heating job on a staple up system.
I know when using Viega pex tubing on a staple up job they recommend using aluminum heat transfer sheets.
Are aluminum heat transfer sheets needed with the Watts Onix tubing?
Any drawbacks to using Watts Onix radiant pex tubing?
  • kcopp
    kcopp Member Posts: 4,695
    If its the Onix that is the epdm rubber stuff w/ the so called O2 barrier in the jacket.
    Don't do it.
    I have seen too many issues w/ it in systems I service. I have plenty of pictures....
  • Zman
    Zman Member Posts: 7,614
    I have never used Onix. I think that type of tubing has some baggage (probably unfounded) from failures of similar products.
    There are very few applications where plateless staple up is a good plan. If you are willing to run high supply temps, you can get <12 btu/foot out of it.
    I see you referred to Watts Onix radiant pex tubing.
    To be clear Watts Onix is EPDM. Watts also makes pex and pex-al , very different than Onix.