It's Selfie Thursday, look at our special barometric damper

GW
Member Posts: 4,925
Dang boiler was pulling an 06, no wonder.


0
Comments
-
Real time saver for those who can't work a pair of snips. I bet the boiler/furnace was nice and clean with the high neg draft...
There was an error rendering this rich post.
0 -
The sad part is this is off of a Bud g215 with a Riello gas gun----meaning-- the original guy may have goofed it, but the guy that put the MG-1 damper on sure would have seen this. Two knuckle headers in a row.0
-
With a gas conversion burner, shouldn't the regulator be on the run with a spill switch?0
-
Yes my smiley pic is without the barometric damper and spill switch. My guy took this piece out and added a piece of 6” and a 6” tee.; the barometric wasn’t the problem. I guess my subject title isn’t super accurate. He brought his back to the office knowing I’d be tickled0
-
Only if it's an atmospheric type or one with a standing pilot light. On a power burner with electric ignition, the setup in the pic is correct as long as the hole in the smoke pipe is full size and a blocked-flue spill switch is used.HVACNUT said:With a gas conversion burner, shouldn't the regulator be on the run with a spill switch?
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting-1 -
Are you saying the baro was installed without cutting in to the flue?0
-
This was how we found it, yes it did have a barometric damper on it. The damper wasn’t the problem through. This little hole was the problem. We installed a tee (yes we could have cut out the hole to match the damper)1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 55 Biomass
- 423 Carbon Monoxide Awareness
- 102 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 102 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 935 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements