Venting Wet Returns

cdm
cdm Member Posts: 77
I have seen several posts on venting wet returns on one pipe steam systems - What advantage does this add one pipe steam system.

cdm

Comments

  • Large vents on the dry returns allow the air to escape so the steam can get in. The radiator vents are too small to handle this job, without burning excess fuel to force the air out.—NBC
  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    But there's no point to venting a wet return -- if that is what it really is.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Fred
    Fred Member Posts: 8,542
    @cdm , I think those posts you refer to are from someone who thought/thinks venting a wet return helped their situation. Don't vent a wet return. It is a waste of a good vent and likely will spew water. Serves no purpose.
  • cdm
    cdm Member Posts: 77
    Thanks for the response - Since the wet returns are at the end of the main last feed. I also could also not see why an additional vent was required.

    cdm
  • Fred
    Fred Member Posts: 8,542
    Let's make sure we are really talking about a wet return. A wet return is a return that is below the water level in the boiler. Any returns above the water line or at the end of a main, after the last radiator run out is basically a "Dry" return and can benefit from venting. Once it drops down and is below the boiler water level, it is filled with water and there is no benefit from venting those wet returns.