steam boiler eg series weil mcclain -water hammer issues -heats fine-no main air vent-no insulation on mains
0
Comments
-
stop the water hammer,
enjoy the heat,
add main venting,
and insulate your mains,
So,
we're gonna need more info,
a large picture of the boiler and the piping above to the ceiling,
what pressure are you set to, and what's the highest you see on the gage?
picture of the gage and pressuretrol,known to beat dead horses0 -
Seems like @neilc 's got it, except that it's in reverse order -- with one addition: before you start insulating your pipes, which you must do, check the pitch of every single near horizontal pipe you can find. They all must pitch uniformly to where water can drain back to the boiler, either through a wet return or directly. No sags. No level pipes. And that check is a lot easier to do before the pipes are insulated.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements