one pipe steam boiler water hammer

steam boiler eg series weil mcclain -water hammer issues -heats fine-no main air vent-no insulation on mains

Comments

  • neilc
    neilc Member Posts: 2,854
    stop the water hammer,
    enjoy the heat,
    add main venting,
    and insulate your mains,
    ;)

    So,
    we're gonna need more info,
    a large picture of the boiler and the piping above to the ceiling,
    what pressure are you set to, and what's the highest you see on the gage?
    picture of the gage and pressuretrol,
    known to beat dead horses
  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    Seems like @neilc 's got it, except that it's in reverse order -- with one addition: before you start insulating your pipes, which you must do, check the pitch of every single near horizontal pipe you can find. They all must pitch uniformly to where water can drain back to the boiler, either through a wet return or directly. No sags. No level pipes. And that check is a lot easier to do before the pipes are insulated.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • neilc
    neilc Member Posts: 2,854
    edited February 2018
    ;)
    well I did say stop the hammer first
    @Jamie Hall
    known to beat dead horses