Figuring out proper radiator size for a room... in laymen's terms

bipbap
bipbap Member Posts: 191
I'm trying to figure out if I can downsize the radiator in a room.
What's the easiest way to do the calculations for a newbie?
It's a small room and I'd like to go from a 13-fin beast of a radiator to a 6-fin.
One-pipe steam system.
Thank you!

Comments

  • Ironman
    Ironman Member Posts: 7,511
    The only accurate way is to do a load calc on the entire house and then on the room individually. If the radiation for the entire house is over-sized by 15%, then it should be over-sized for the room proportionately.

    IDK why you'd wanna go to the trouble of changing the rad, though. Just slow down the vent rate on it.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Mike Cascio
    Mike Cascio Member Posts: 143
    Easiest way to fix this problem is to slow down the vent. A gorton #4 is a great way to keep an oversized radiator tame.
  • Brewbeer
    Brewbeer Member Posts: 616
    Is the room overheating, or are you trying to gain space by downsizing the radiator?
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
  • bipbap
    bipbap Member Posts: 191
    Mostly swapping to regain some space in a small room while still making sure adequate heat.
  • bipbap
    bipbap Member Posts: 191
    Is it possible to just do a calculation on the room size vs size of radiator?
  • Ironman
    Ironman Member Posts: 7,511
    bipbap said:

    Is it possible to just do a calculation on the room size vs size of radiator?

    I think you missed what I stated earlier about it being sized PROPORTIONATELY.

    If you only do a load calc for that room and it needs 10k btus, and then you install a radiator with 10k btu output, what's gonna happen if the rest of your radiation is over-sized by 30%? Answer: that room will be under-radiated by 30%.

    This is why you need to do a load calc and radiation survey on the entire house.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.