Singing Snowmelt
JMA
Member Posts: 1
Long time reader, first time poster. Have a commercial snowmelt system served by 8 150,000 BTU wall hung, fin tube, mod/con boilers. The boilers are cascaded together and individual units come online and drop off as necessary according to system demand. After two months of operation each boiler sings - high pitched harmonics - as soon as it hits approx 90% firing rate - outlet temps are around 80 to 90 degrees at this point. Once the set point of 130 degrees is reached the boiler modulates down past 90% firing rate to maintain a 20 degree delta and the noise goes away. System was thought to be mixed to 30% glycol but one last zone has not been brought online so it was discovered that the mix is around 45%. We were able to make the noise go away using larger more expensive boiler pumps but the calculated flow rate difference between pumps was minimal - approx 11gpm with the smaller and approx 16 gpm with the larger. We are in the process of lowering the glycol mix for the current system - last zone won't go online until next winter - and hope that helps because the cost for 8 of the larger pumps is not pretty and not sure we want even more flow going through the boilers. Thoughts?
0
Comments
-
-
What boiler? Any possibility of a HX that would allow you to not have to run glycol through the boilers?
0 -
I assume all the boilers had a combustion analysis done on them.0
-
-
Sounds like steam is being made or no combustion test. Who designed the system including the loops, boilers, piping and pump selection?0
-
Are the boilers piped via a hydraulic separator or Primary secondary. Each boiler needs to have adequate flow, and use the glycol derate info, usually no the bucket, to select the circ.
With a high glycol% you could require 30% more circ compared to water.
Or it could be a combustion noise. Check venting lengths, was a combustion analysis done?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
When the noise correlates to the modulating burner, my first thought is further tuning is needed via combustion analysis and adjusting the throttle.
As far as glycol, I use the premixed Rhomar RTU45 - more of an exact science.Steve Minnich0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements