Trane Invisible Radiator - repair

JMSullivan
JMSullivan Member Posts: 6
edited January 2018 in Strictly Steam

My house was built in 1935 and contains invisible or concealed radiators in all rooms. Several of the radiators do not heat. Is it possible to repair this type of radiator (I believe I have Trane Invisible Radiators - based on the literature posted on this website) without taking out the wall? All contractors that have looked at these radiators believe the only way to "repair" them is to take apart the wall and "have a look around"

Does anyone have experience with this type of radiator?

Please note, I am a homeowner (not a contractor nor a successful DIYr)

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,840
    What is wrong with the radiator that the contractors think they need to rip open a wall to look around?

    The radiator allows water to flow through it to emit heat. Basically a glorified pipe. If you aren't getting flow 9 out of 10 times the radiator isn't the problem and the problem is elsewhere in the system.

    As near as I can tell "digging around" will accomplish one thing, destroying your house.

    Where are you located, we may know a qualified contractor in your area that can actually help you.

    Also here is some information about those units
    https://www.gwgillplumbingandheating.com/webapp/GetFile?fid={147F7FA3-3A99-470D-B6F5-B1545E40406A}
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • unclejohn
    unclejohn Member Posts: 1,833
    I would start with removing the grill and looking for a air bleed. Also there is or was a damper that was controlled by the knob they may have fallen down.
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Before removing the grill I would score the edge of it with a box cutter blade. This would minimize the paint damage to the wall.

    If you do not see an air bleeder or the air flow damper mentioned above, you can buy an inspection camera with 3-4' lite flex end for about 100 dollars. This would let you find things even without grill removal by going up the bottom.
    There may be valves that are shut off stopping the water flow.
    You might see or feel these thru the bottom opening.
  • ScottSecor
    ScottSecor Member Posts: 902
    Sneak a small camera or cell phone under the bottom and snap a few photos (especially near the ends), might tell you more without much effort. Might be able to do the same from the top.
  • Steamhead
    Steamhead Member Posts: 17,387
    Hang on, gentlemen- is this a steam or hot-water system?

    I don't see an air bleed in the usual place, so it may be steam. @JMSullivan , if you're not sure, can you take a pic of the boiler and post it here?

    Around here, we see lots of these Trane Invisible Radiators on Vapor steam systems. These are either Orifice systems, or there are thermostatic traps on the return connections.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
    JUGHNE
  • JMSullivan
    JMSullivan Member Posts: 6
    edited January 2018
    Thank you all for your comments.
    Based my "reading" of Dan H's books, I have determined that I have a 2-pipe steam system. When originally installed in 1935, the boiler was coal fired. It was upgraded many years ago to a gas boiler. I will take a picture of it and post soon, if that will help.
    I am located in Winston Salem, NC
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    Most likely you have some bad steam traps then. Take 1 grill off and also look in the bottom and poke around with a flashlight, mirror, camera etc
  • JMSullivan
    JMSullivan Member Posts: 6
    Below are pictures taken of a radiator in a different room. Same type (Trane Invisible Radiator) but located in the paneled den.
    I am not sure what an Orifice or Thermostatic trap looks like - do I have one?

    I have tried to provide a representative example of the radiator - left side top and bottom, right side top and bottom, and outside.

    Any thoughts are welcome!
  • Steamhead
    Steamhead Member Posts: 17,387
    Looks like the device in the "leftside" pic is a steam trap. Is the top of that device just flat or slightly rounded, or is there a knob sticking out of it?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Danny Scully
    Danny Scully Member Posts: 1,440
    Almost looks like a Veco trap right @Steamhead?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    Unfortunately getting at it is the problem and the convectors need cleaning badly. The cleaning can probably be done in place.

    Wonder if it is possible to disconnect the supply and return in the basement, back the risers out and remove the convector for access to the trap and for cleaning the fins then reinstall without opening up the wall?? Wouldn't be easy

    Or clean in place and if the trap is failed open, leave it in place and install a new trap in the basement.#####

    #####not sure I like my own idea!!

    Either way is not easy
  • JMSullivan
    JMSullivan Member Posts: 6
    Thanks all! One more fact I forgot to mention...some of the radiators are on the second floor and the boiler is in the basement. Therefore if I am understanding the "removal" process mentioned by EBEBRATT, I am not sure all the pipe could come out.

    I have taken better pictures of the left top and left bottom of the radiator. I believe the trap is on the bottom, correct? To answer STEAMHEAD, I believe the "top" is flat-ish. It has a slight dome on top but the top of the dome is flat.

    I also noticed on the top left a "pokey up thing" Is that something important?

    Lastly, do I just vacuum the fins? Or is there something else I should be doing?
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    Your last two pictures, 1 is a steam trap. The other one is a pipe plug. I would use a vacuum and get out as much as possible. Use something like a hacksaw blade to poke the stuff out between the fins. If you can get them reasonably clean ok. If you need to do more a couple of shallow "cake pans" under the convector and a spray bottle with water will clean them out. A few rags and a wet dry vac will clean up what misses the pans.

    Yes, your second floor units will be more of a problem. You may have to cut and patch the walls on some of them
  • JUGHNE
    JUGHNE Member Posts: 11,279
    How about pictures of the rads that show the wall about 2' each way. An angle shot of each end.
  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    How are the inoperative radiators related in terms of location?
    This could be the result of one trap which, having failed open, and flooding the common return with steam, shuts the traps on the neighboring radiators.
    Sometimes the pressure can creep up, and cause one weaker trap not to close, so checking the pressure would be a good place to start. Pictures of your boiler piping, and controls would help.—NBC
  • Phil53
    Phil53 Member Posts: 73
    Not sure but maybe the wall opening behind the baseboard is large enough to get at the unions and remove the convector. It would make sense to allow for maintenance. I guess the only way you'll know is to remove the base shoe and baseboard.
  • KC_Jones
    KC_Jones Member Posts: 5,840
    I'd take the trap out. Cutting into those walls shouldn't even be considered as an option. It's pretty obvious that trap has been changed unless it has miraculously aged differently from everything around it. Also I doubt they used a merchant coupling in 1935. I could be wrong, but looking at those pics that's how it looks to me.

    Get an appropriate sized offset wrench, undo the union nut. Remove the escutcheon plate for clearance, get a pipe wrench on the pipe and an appropriate sized wrench on the trap and take it out.

    Wouldn't be easy, but for me cutting holes wouldn't be an option ever.

    I find it hard to believe they didn't think about maintenance. Sometimes that requires specialty tools.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Fred
    Fred Member Posts: 8,542
    I'm betting the intent was to take the unions loose from the bottom and lift the convector out by taking the vent cover off and lifting it out through that opening. Look at the width of the border around that vent. The sides are twice as wide as the top and bottom and it is wider than the opening in the baseboard.
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Are these completely flush with the rest of the wall or do they stick out some?
    The angle pictures would show that.
    If the base/trim is just a short 3-4' length then may the intent was to carefully remove the trim to get to the unions.
  • JMSullivan
    JMSullivan Member Posts: 6
    Thanks for your thoughts! I will try to answer all questions...starting with @nicholas bonham-carter : My house is a two-story brick georgian with a center hall. Two bedrooms (two radiators per room) on the second floor do not heat. These bedrooms are two stories above the boiler room. The center hall radiators also do not work. (1 in the second story hall and 1 in the first floor hall) The radiators furthest from the boiler work.

    Please refer to attached pictures of the boiler...not sure where the pressure gauge is but currently the boiler is not running (too warm now!)

    I have attached angle pictures as well. Notice, there appears to be nails that are attaching a "flashing" around the convector/fins/radiator. In poking the ruler around, it does not appear to have any room around this element. Therefore, I am not sure the convector/fins/radiator can be removed.

    @KC_Jones - I agree with you! I have been asking about specialty tools and keep getting the "eye roll"

    I have also attached an "outsideangle" picture with shows everything is flush with the wall.


  • Fred
    Fred Member Posts: 8,542
    I'm sure the flashing is attached/nailed to the walls. I'm also equally sure the convectors are not. They are likely suspended in the cavity, supported by the piping. The bottom has to be open to allow air flow, so there is not even a pan there that the convector would drop into.
  • gerry gill
    gerry gill Member Posts: 3,078
    Looks to me like you should be able to get those traps out and rebuild on a work bench.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    Seeing these new pictures I was hoping for more wiggle room. My eyes hurt looking at it. Doubt those traps have ever been out. To me it's inacessable. I think they built around it with no means for practical access
  • Neild5
    Neild5 Member Posts: 181
    > @KC_Jones said:
    > I'd take the trap out. Cutting into those walls shouldn't even be considered as an option. It's pretty obvious that trap has been changed unless it has miraculously aged differently from everything around it. Also I doubt they used a merchant coupling in 1935. I could be wrong, but looking at those pics that's how it looks to me.
    >
    > Get an appropriate sized offset wrench, undo the union nut. Remove the escutcheon plate for clearance, get a pipe wrench on the pipe and an appropriate sized wrench on the trap and take it out.
    >
    > Wouldn't be easy, but for me cutting holes wouldn't be an option ever.
    >
    > I find it hard to believe they didn't think about maintenance. Sometimes that requires specialty tools.

    If an ofsfset wrench doesn't give enough swing crow foot wrenches are also available. 1/2 drive goes up to 2 9/16, and 3/4 drive goes even bigger. Yes they are pricey but way cheaper than cutting open walls.
  • Neild5
    Neild5 Member Posts: 181
    I would look at crow foot wrenches, they go big enough and would not require opening the wall. Imperial Newton makes them up to like 6 3/4 inch.
    KC_Jones
  • JMSullivan
    JMSullivan Member Posts: 6
    Thank you Everyone!!!
  • unclejohn
    unclejohn Member Posts: 1,833
    I'm betting on cutting the wall. Second dollar risked.
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Wouldn't just removing the baseboard trim carefully....(air inlet part) get you to the trap?