I put in Gorton 1s since the pipe is near the ceiling I am afraid that it will ruin the wood
acl10
Member Posts: 349
I put in Gorton 1s since the pipe is near the ceiling I am afraid that it will ruin the wood. When the boiler is on moist air comes out and it could rot the wood after a while. What does everyone else do about this problem
0
Comments
-
Moist air while the system is venting? Shouldn't be a problem- as long as they close when steam enters them.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Are we talking fine finished wood or typical rough basement floor joists with bare lumber above?0
-
If it becomes a problem which I doubt, the vents can be piped in high up on the vertical pipe coming down from the return. I don’t think you will have a problem though, except the venting capacity may not be adequate. Ideally, you need roughly one Gorton #1 for each 10 feet of 2 inch pipe.—NBC0
-
Bare lumber. I felt the moist hot air coming out. Wont that rot the wood over time0
-
The moist air should stop when the steam gets to the vent.
The same amount of air will be passed regardless of the vent size. A larger vent would get it over with quicker.....the whole purpose of being big.
If it passes more than a whisper of steam then you have a problem.
The moisture on the wood should dry up quickly.
There are houses that have had this happen for 80-100 years.
Yes, if it blows steam you could see some damage, but for the most part maybe just some discoloration.0 -
Here are pictures of the two sets of vents. These were installed on two separate pipes at the end of the main in the meter room.
On each I put one Ventrite 75 and one Gorton 1 on a 3 inch high pipe.
0 -
Screw a piece of sheet metal to the underside of the floor- donegwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
-
Another problem I have is that after they vent the air they fill up with water and leak on the cement floor> i had this when I had Gorton ds and now that I changed them to 1s they are still spurting water after they finish venting air and the condensate comes back. I dont real have a better place to put the vents because the rest of the basement is finished.0
-
It's a bit hard to tell for sure from the pics, but I think you have a slope issue with your vent piping. All the vent piping needs to slope back towards the main piping. It appears you have the pipe tapped on the lower portion of the main which would cause that nipple to run uphill towards the main.
Also with the tee the way you have it, one is slopping towards the main one is sloping away. If you cause water to sit in those pipes the water will constantly be shot towards the vent, cooling it down and opening it up and then it spits.1 -
Can I install a Gorton 1 at an angle like a 45 degree . I want to put in on a longer pipe and extend it it will still drain back or does it have to be strait up0
-
It should be installed as vertical as you can get it, at 45 degrees it will probably spit a lot because all the water can't drain out of it.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
I can't tell from the pictures, but are those vents just tapped into the side of a pipe? Maybe thats why they spit.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
One is tapped on the side and one on the pipe going up. I think one of the Gortons that was leaking is defective because when I turned it over and blew into it it didnt shut. I will change it and see.
I put the ventrites on the pipe tapped on the side and they dont leak.0 -
Normally these are near the boiler, so the air up there is fairly warm, so no risk of condensation on the wood. The sheetmetal idea is good. But otherwise I wouldn't worry about it. Old growth lumber form before 1940 is almost as good as treated lumber now. Most basements before the invention of humidifiers were typicality very, very damp.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements