All radiators are hot but boiler still runs for a long time (90-150 mins)
ImYoungxD
Member Posts: 130
System is one pipe
I replaced the main vent with Gorton 1 soon to be replaced with Big Mouth
All radiator vents are replaced
I have a 0-5 PSI gauge with new brass pigtail and pressuretrol cut in 1, differential 1.5. 30 PSI gauge works well.
Boiler was oversized but tuneup guy changed nozzle from .75 x 45B to .65 70B and did not run combustion analysis. Had water hammer but no more now. I am making sure the next tuneup guy has an combustion analysis.
Planning to insulate mains later.
The issue is that my boiler runs for at least 90-150 minutes until the pressure reaches 1.5 then turns off. All radiators are hot (200f+) at 30-45 minutes. Is the boiler wasting oil or is how is it's supposed to be? I should mention that when the PSI is between 0.7-1.5, one or two of the 1st floor vents hiss and close (ping noise). They are Hoffman 40. Maybe vents are defective?
Thanks
I replaced the main vent with Gorton 1 soon to be replaced with Big Mouth
All radiator vents are replaced
I have a 0-5 PSI gauge with new brass pigtail and pressuretrol cut in 1, differential 1.5. 30 PSI gauge works well.
Boiler was oversized but tuneup guy changed nozzle from .75 x 45B to .65 70B and did not run combustion analysis. Had water hammer but no more now. I am making sure the next tuneup guy has an combustion analysis.
Planning to insulate mains later.
The issue is that my boiler runs for at least 90-150 minutes until the pressure reaches 1.5 then turns off. All radiators are hot (200f+) at 30-45 minutes. Is the boiler wasting oil or is how is it's supposed to be? I should mention that when the PSI is between 0.7-1.5, one or two of the 1st floor vents hiss and close (ping noise). They are Hoffman 40. Maybe vents are defective?
Thanks
0
Comments
-
Could well be running just as needed. The radiators need to stay at temperature long enough to heat the space... I just posted a paper on the topic!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Why was the nozzle size changed? Was the boiler over-sized and short cycling?0
-
@Fred plumber probably knew the boiler was oversized (120,400~ BTU). It was short cycling after I cleaned the pigtail and made adjustments to the pressuretrol (thanks to your guide). No more steam/water hammer as well after he changed the nozzle but no combustion analysis was done. I was questioning on why the burner stays on for so long but it looks like it's a normal process.0
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements