circulator pump - Single speed vs 3-speed vs variable
hal1000
Member Posts: 8
in Gas Heating
Is there any downside in getting a 3 speed or variable speed circulator pump over a single speed?
0
Comments
-
One possible downside is the new circulator may not be the right one for your application. Need to know more about the system to select the correct circulator.Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg0 -
Single speed PSC circs rarely meet the needs of any system without loads of accessories that may or may not be spec'd correctly . 3 speed circs are a bit more versatile in that you have 3 performance curves to work with , odds are better of having the right size circ Xs 3 . VS circs are best . Just look at the performance curves to insure they have the capability to do the jobYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331 -
What are symptoms that a circulator is undersized? Oversized?0
-
What is your intended use for the pump?
CH, DHW, etc...?0 -
Before assessment of circulator sizing. You need to know the flow rates the system needs. From that system head loss calculations need to be done. Only then can you properly size a circulator.
It could be entirely possible that a happy medium need be chosen if the system piping can not manage the flow rates needed.
Is the system zoned?
If so are zone valves, or are circulators used?
Symptoms of over sized circulator is velocity noise, low delta.
Symptoms of undersized circulator trapped air, high deltas, boiler shutting down on high limit.
Just a few. It depends on what the circulator needs to be doing in the system.
PSC
3 speed
Delta t
Delta p
VS
They all have a place
0 -
I think any circulator replacement or upgrade should warrant a properly sized ECM. Some versions , like the B&G Varios which have a 7 speed selector have a very wide performance range.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
hot rod said:
I think any circulator replacement or upgrade should warrant a properly sized ECM. Some versions , like the B&G Varios which have a 7 speed selector have a very wide performance range.
Ecm selection is getting better, but there are still a lot of voids to Be filled that older systems have. Especially single zoned higher flow, and head systems. They are making progress.
0 -
@Gordy
Is the system zoned? No. I have 1 circulator that flows into 2 loops. There are no zone valves and only 1 thermostat...each loop spans both floors - one loop is for the south half, one loop is for the north half.
I believe my current delta is 10F. I've never heard any noise from the pipes. Each season, I do get some air in the top radiators.0 -
What is your goal in circulator replacement. If things are working fine?0
-
I see you have another thread going. Which sounds like a balancing issue. Increasing flow may, or may not help. Could make things worse. I would try balancing rads as suggested. See how that works. If not maybe splitting the two loops, and installing a smaller circ on each.0
-
@Gordy Could one boiler serve 2 loops and 2 circulators? All on one zone? How would that be piped? My current system is one circulator flowing into the boiler.
Boiler -> supply pipe --> splits into 2 supplies --> comes back as 2 returns --> joins to 1 return --> expansion tank --> 1 circulator --> boiler
0 -
Sure it would be two zones so a second thermostat would be needed, and a zone controller.0
-
I would try the balancing first however. Another option would be one circulator with two zone valves. The circulator would be a ECM delta p variety, or your existing with a differential bypass.0
-
@Gordy I see. So 2 thermostats, 2 zone valves, 2 circulators. Most likely, I would set both thermostats to the same temperature. Each zone would span 2 floors (north vs south halves)...it seems like a lot of work to ensure the loops both get adequate flow..
As you mentioned, balancing each radiator individually is one idea..any other ideas ?0 -
It would be either or. One circ two zone valves, or two circulators.0
-
With a 10 delta your getting good flow. How are you measuring delta, and where?0
-
Can you post photos of the piping in the vicinity of the circulator and where it splits into two loops, and of the radiators with the valves?Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 50 Biomass
- 419 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements