retrofit honeywell cs82a matchbook powerpile wall furnace
wuoshi1031
Member Posts: 1
in Gas Heating
Hi everyone, I recently came across this faulty William Furnance using a milivolt gas valve system.
Upon some trouble shooting, it seems the thermopile is only putting out ~450 millivots
The gas valve opens and fires up fine when I by pass it with 1000 milivot used battery.
Question is: I can't seem to find a replacement thermopile in this style (honeywell cs82a matchbook powerpile)
Does anyone have any recommendation for a comparable replacement? I am thinking retrofitting it with Robertshaw 1820-019 PG9 Left Hand Pilot Generator and Thermopile. Is there a difference between left and right hand pilot?
Anything to watch out for with the retrofit? I looked up some old forum posts and noticed that some member suggest a possible pilot light turn down and main burner turn down....
any help would be greatly appreciated
Upon some trouble shooting, it seems the thermopile is only putting out ~450 millivots
The gas valve opens and fires up fine when I by pass it with 1000 milivot used battery.
Question is: I can't seem to find a replacement thermopile in this style (honeywell cs82a matchbook powerpile)
Does anyone have any recommendation for a comparable replacement? I am thinking retrofitting it with Robertshaw 1820-019 PG9 Left Hand Pilot Generator and Thermopile. Is there a difference between left and right hand pilot?
Anything to watch out for with the retrofit? I looked up some old forum posts and noticed that some member suggest a possible pilot light turn down and main burner turn down....
any help would be greatly appreciated
0
Comments
-
I want to help you but am going through a computer problem that encrypted all my files. If you call me at 401-437-0557 I can get your mailing address and send you a complete step by step procedure to replace the CS82 pilot. Call 401-437-0557 I will be in all day due to snowstorm.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements