Gv90 short cycling be and slow to heat house
Rob_55
Member Posts: 35
New install. Gv90+5. Baseboard. Two stories. 3 zones. 2000sq ft.
Didn't notice lack of heating until recent crazy cold temps. House normally at 65. Set to 70 and after a few hours it was only at 68. Noticed boiler would cycle on and off but thought it was just the circulator / energy savings routine.
Watched it go through a cycle. Start at 150 degrees. Cuts off at 175 after a few minutes of heating. Drops rapidly back to 150 as circulator runs and flame is off. Raised temp knob to 185 from 180, but not much improvement. Also noticed electrical beeping after I raised temp. Got the guy who installed it coming tomorrow, but just curious what you all thought.
See video of the heating cycle. Weird beeping st 2:52
https://photos.app.goo.gl/kkVtZqEK3c3mQm8v1
Didn't notice lack of heating until recent crazy cold temps. House normally at 65. Set to 70 and after a few hours it was only at 68. Noticed boiler would cycle on and off but thought it was just the circulator / energy savings routine.
Watched it go through a cycle. Start at 150 degrees. Cuts off at 175 after a few minutes of heating. Drops rapidly back to 150 as circulator runs and flame is off. Raised temp knob to 185 from 180, but not much improvement. Also noticed electrical beeping after I raised temp. Got the guy who installed it coming tomorrow, but just curious what you all thought.
See video of the heating cycle. Weird beeping st 2:52
https://photos.app.goo.gl/kkVtZqEK3c3mQm8v1
0
Comments
-
Someone here that is familiar with that boiler could answer if those pumps should be pumping up or down.
There have been some pump issues mentioned here today.0 -
Rob, could you do a video of your piping and pumps. (Move slow for old people please)
I had the early version of this boiler and the inlet and outlet were clearly marked on it. Don't know about the later generation that you have.0 -
Here's a video of the plumbing. Hopefully video is slow and steady enough
https://photos.app.goo.gl/92m6zJbX1TVQELPy10 -
Also, I have the outdoor sensor0
-
IDK, there were no inlet/outlet labels on the boiler?
You should have the manual that came with this boiler.
It includes typical piping diagrams, perhaps not as involved as your piping but give the basic concepts.
Pumps have arrows on them indicating direction of flow.
Someone here can just look and know.
0 -
Looks like flow is correct. See attached0
-
There should be a big label on the side of the boiler that shows the connections.
The return goes to the secondary heat exchanger.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
The boiler primary/secondary tees seem a bit far apart.-1
-
I think his book says 12" max.
What started me on this crusade was the first video, when I paused it I could see 2 pumps pumping towards the boiler.
It is actually the pumps on the return pumping into the boiler rather then away after the boiler towards the zones.
That isn't quite right but doubt if it is the cause of the problem.
Maybe a control issue with the boiler mixing valve?0 -
@Rob
The boiler that you have can offer up 119 KBTU net.
The question that begs is whether the house can actually utilize 119KBTU. It would require you to have approx. 238 feet of element for the baseboard. This is impossible in a 2000 square foot house. This explains your constant cycling.
It' is, unfortunately, the typical situation of the "contractor" installing a boiler that is double the size necessary.
Ask the guy who installed it whether he ever did a heatloss on the house before selecting this boiler. See what he says.1 -
Approx 140ft of baseboard + 50gal indirect super store water tank. My boiler gv90+5 is 113kbtu. Sounds about right based on what I read online. I'm pretty sure I watched him measure for this.0
-
-
Ok..So assuming it is oversized, why won't my house heat up?. Baseboard barely gets hot. Wasn't a problem when it was warmer out as I could feel the heat coming off the radiator?.0
-
Try turning the "Economy" setting on the control module to the "Minimum" setting. See if there is any change. Keep us posted.0
-
I would also look at those pumps and see if they are blinking.
Happened again on a different job yesterday. Got there and found 2 zones blinking, its weird the 1 1/4" spirovent just sits there, I remove the head clean it and wham, it works again.
If you have the outdoor sensor, then the boiler will adjust the water temp based on that and some times that setting will be too low for the amount of heat that is required in the space.Tom
Montpelier Vt0 -
Thanks everyone. One other thing that occurred recently was a water main break on our street. Not sure if losing water would do anything (air in lines).0
-
If the boiler's over-sized, it can short cycle. IDK if that boiler has an anti short cycle timer. If it does, it's gonna hold the burner off for a minimum time, during which, the SWT to the rad's will cool down. They loose their heat output as that happens.Rob said:Ok..So assuming it is oversized, why won't my house heat up?. Baseboard barely gets hot. Wasn't a problem when it was warmer out as I could feel the heat coming off the radiator?.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
What's the water pressure on the boiler gauge?Rob said:Thanks everyone. One other thing that occurred recently was a water main break on our street. Not sure if losing water would do anything (air in lines).
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
18psi
Beeping noise was coming from one of the circulator pumps.0 -
@ Rob
The reason the boiler won't heat your house is as follows:
The boiler operates with a 25F differential. This means it goes from 155F to 180F for each cycle. Notice, however, that it spends far more time between 165F and 155F as compared to the time between 180F and 170F. So, we can estimate that you have an AVERAGE supply temperature of about 165F when taken over the time interval.
Now, we must look at the average water temperature at the baseboard which is typically 6 degrees less than the supply water temperature: 159F.
This will not heat the house on a very cold day.
So, raise the boiler temperature high limit to 200F (boiler maximum). Then, the average water temperature at the baseboard will be approx. 179F and that will heat the house.
For efficiency in "normal" cold ambients, reduce the 200F value back to 180F and further reduce it to 160F in the shoulder seasons.
0 -
Thank you0
-
You're welcome.
And, because the boiler is so severely oversized, I would recommend that you get the "guy who installed it" to combine the three zones so a single thermostat (in the coldest zone) calls all three zones simultaneously. Have him install a globe valve in the two hottest zones and then monitor the temperatures. If either of the two hottest zones climb higher than desired, you throttle that zone with the globe valve to reduce the flow rate slightly. This takes some patience as the adjustments must be minute and the time to observe the outcome must be several days. Note that this approach is only valid for buildings that have reasonably proper balance between zones. It will not work if one zone is severely overradiated as compared to the other zones.
1 -
Turns out I had a bad water temp sensor. Temps are warm today, so we'll see what happens when it drops to teens tonight0
-
The clip on return water temperature sensor?0
-
make sure to turn the boiler back down to 180. You should have no issues now..0
-
Yes the return water sensor clip on0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements