Asking again
Memoose
Member Posts: 2
Ok I just got a gas boiler to replace my oil boiler. It’s a Westinghouse wbrc140 It has a internal circulator on the supply side. I added a few more baseboard radiators in the second floor considering it never had heat. Alas here is my issue, it’s a mono flow system,to start. The heat does flow to the second floor, it just seems to take a lot longer then I anticipated. Question is with the circulator on the supply side, may I, can I, should I, or not add a second circulator on the return side to help pump faster. I should add it’s all one zone up and down work on one t stat.
0
Comments
-
Did it heat faster with the oil boiler ?Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg0 -
How did you pipe it? it should be piped primary/ secondary.0
-
Two pumps in series is a very poor idea. If you need more flow capacity, a bigger pump is a much better idea.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I find the 008 works real good on monoflo. more gpm...how about a picture of the boiler to see how its piped? The other question, is it using out door reset and did the curve get set or is it factory?0
-
Look at all the Geo pump packs that have two pumps in series.0
-
But there is not a boiler between them, would that be different?0
-
How long is " A lot longer". The second floor is the furthest away from the boiler, sometimes patience is ok.0
-
I should be more precise. Two pumps in series is OK, provided they are properly matched. Likewise two pumps in parallel. However, if a system -- such as it might be a radiant piping set of loops -- needs a pump, the simplest and most reliable solution is one pump with the needed head and flow capabilities.
Without getting into a dissertation here, any pump installation must concern itself with the net absolute pressure at the inlet to the pump. If you have two pumps, one at the inlet to a pipe system and one at the outlet, there is a real risk that the one at the outlet may not have that pressure required, unless (in a heating system) that is the point of no pressure change.
There are too many possible configurations to give a general answer. However, the fundamental question is -- why bother? With the wide range of pumps available, surely one could find a single pump which matched the system.
The only time I have used two pumps in series -- and I have -- was in a situation where I simply could not find a single pump with adequate head. It was a slightly unusual situation; I needed to pump -- as I recall -- about 200 gpm up an elevation difference of about 3500 feet... that installation got an intermediate 15 stage turbine at the 1700 foot level installed in a surge tank.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I'll repeat what was asked......how did you pipe the added baseboards?0
-
Using mono flow t’s I spliced the upstairs in the supply side. The current circulator pump is factory installed from Westinghouse.0
-
That won't work. Too much pressure drop in the new zone.
Repipe it so the new zone has its own circulator and add a flow-check to each zone.
Maybe it's time to call a pro. Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements