Dew Point Control for radiant cooling
KVieira
Member Posts: 5
I'm doing a geothermal w/ radiant cooling. I need a control to keep the radiant cooling above the dew point to prevent condensation from forming? Who make a dew point control for this?
0
Comments
-
Google: Weiss Instruments.
Their are others.
If you need application help
Try Kele Associates in TN. They sell controls and can give you some help
The Weiss control looks simple and should work0 -
I think tekmar has a t-stat that calcs it from outdoor temp."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Tekmar has the 553 communicating thermostat that has a built in humidity sensor. It marries well with the new house control, 406 I believe. The water temp is then always kept 2 degrees above dew point. This setup is for a 2 pipe heating/cooling system. If you want to add air conditioning to work in concert with the floor cooling, you need the 557 thermostat to control the fan coil and set the rest of the 553's as part of an air group.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements