Boiler pressure rising, new xp tank and new prv
wasabi85
Member Posts: 3
Hi guys, figured I’d reach out because I’m getting progressively more and more stumped on this issue...
I have a boiler we installed well over a year ago. New trim kit, brand new everything (prv, backflow, Air scoop, xp Tank etc). Dunkirk Cast iron with radiators. And my boiler pressure keeps reaching 30 psi and tripping the relief valve. I’ve checked the Expansion tank and the diaphragm appears to be in tact (no water coming out when I check pressure). I shut the ball valve on my incoming water supply to see if it was an issue related to the pressure rising due to a bad reducing valve, but the pressure keeps rising regardless. Any thoughts feedback or input is appreciated. I didn’t see this thread anywhere because like I said I’ve already checked the Expansion tank unless I’m missing something (which I am obviously - the source of the pressure change)... thanks!
One other piece of information... from room temp cold not firing it goes from 15 psi to 20, then creeps from 20-30 over the period of about an hour.0
I would check the sizing of the expansion tank then check the precharge pressure with the tank isolated.
The indirect or tankless coils are also likely suspects."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
4.4 Gallon / standard 30#, precharge 12psi, charge when running climbs but is at 22psi now matching the boilers pressure... no sidearm, this is a strictly heating only system... wondering if the Expansion tank is too small because it’s a radiator system with a lot of water in it?0
Respectfully all your statements can't be true:
Heating only, no tankless or indirect heater means the only way water can enter the system is your MU water and prv.
You said from room temp cold and NOT firing that the pressure builds from 15-20-30 over an hour (this would show a leaking prv)
You said the pressure keeps rising even with the city water is valved off. (this would show a bad or undersized expansion tank
So not knowing here are the possibilities
So, with no tankless or indirect:
1. Prv leaks by
2. Expansion tank is too small
3. The expansion tank has lost it's air pressure. You must check the pressure on the air side of the bladder with the water side of the tank isolated and drained (0 pressure)
Also, the air pressure in the bladder & the outlet set pressure from the PRv must match
Do you have some type of check valve , flow check or zone valves that can prevent hot water from the system/boiler from getting to the expansion tank??
Got any pictures??0 -
My house...........Gravity conversion, operated for many years with a #30 expansion tank. When the boiler failed, and I replaced it with a smaller boiler, I began having problems with pressure causing the PRV to discharge. I replaced the #30 with a #60 and the problem went away.
Just one possibility, and may not be your problem.0 -
Radiators , pressure increases with temperature rise .. You need an larger expansion tank .. Twin in another #30 same location or replace with #60
- 120 Geothermal
- 169 Indoor-Air Quality