Combustion calculation?
volute1
Member Posts: 2
I need help finding the calculations for combustion air to properly size a louver. We have one 399,000 btu gas water heater and one gas boiler at 1137 mbh. The boiler room is completely enclosed except for a door to the building hallway and one to outside with 4 or 5 1 inch holes drilled through it.
0
Comments
-
The door to the hallway will take air from the room.
Based on somewhat guess work codes, you need 1 sq.in. of opening directly to the outside per 4000 btu. If ducted it is 1 sq.in. per 2000 btu. Unfortunately these openings can be as detrimental as they can be helpful.0 -
Are you a professional trained to work on commercial equipment? If so you may want to look at a mechanical means of providing air. What size is the room in which this equipment is located?0
-
It looks like it will be a 32.4” x32.4” louver to supply enough fresh air for both water heater and boiler for the proper amount of combustion air. Thanks0
-
32.4" X 32.4" louver doesn't have 32.4" x32.4" of free space.
There was an error rendering this rich post.
0 -
Louvers are around .75 free opening I beleive0
Categories
- All Categories
- 85.9K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 420 Carbon Monoxide Awareness
- 78 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 94 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 59 Pipe Deterioration
- 883 Plumbing
- 5.9K Radiant Heating
- 377 Solar
- 14.6K Strictly Steam
- 3.2K Thermostats and Controls
- 51 Water Quality
- 40 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements