hot water!
Daryn
Member Posts: 3
I work in a rural hospital, the building is 5 years old and we have had continued hot water fluctuations. a Bradley S59-3200 mixing valve at my tank is pretty reliable for keeping temp but as it gets out into the building we have some areas that hardly ever get to temp at the faucet??? I've replaced a recirc pump that seemed to help for a short time, but i still have places where i turn the hot water on and its cool for 10 seconds then gets slightly warmer and then just goes cold? It's been a 5 year mystery and drives me nuts some days. Any Help?
0
Comments
-
-
-
What he said. You have a cross connection between hot and cold water some place that needs found and fixed with check valves. A pain to find, but as
Noted usually a post mix shut off valve at the root of the problem. Mop sinks and prerinse sprays are notorious.
METhere was an error rendering this rich post.
1 -
Good info thank you guys! Our as builts are not that great and i have found a valve on the patient floor that was closed and fixed that problem in that area. Surgery and preop are the problem areas now which is coincidentally right next to the kitchen. thanks for the new leads i will keep ya posted.0
-
yeah,
I didn't think about the scrub stations them selves,
are these foot operated?
same scenario, mixed water being controlled by that third valve,
so it could be right in the room itself, one basin to the other,
or room to room,
good hunting,
let us know what you findknown to beat dead horses0 -
From my experience it is always the mop sinks. The chemical man hangs his dispenser on the wall, hooks his hose to the faucet and turn the hot on. All the signage in the world will not keep someone from turning on the cold also which creates a cross connection.
Perhaps some mop sink faucets have check valves built into the unit to prevent this. Sometimes the cold is shut off or the handle is removed.
And it was pointed out to me that keeping the vac breaker on the faucet under continuous pressure is illegal and will remove that level of protection. And eventually keep the vac bkr closed as the check is stuck to the top because of the continuous pressure.
My wife has worked at the same hospital for nearly 40 years, when the toilets are flushing with hot water she tells maint and all the new guys wonder how she knows.0 -
So we have three eye wash station in that wing, i turned them all off and hot water came back. i got rebuild kits coming for them and will hope that is the problem for now.0
-
Often times fixtures like that have point of use mixing valves ASSE 10790. Andn if so that valve should have check valves in the tailpieces.
Just one central mixing valve at the tank is not enough for 100% temperature protection.
Is the valve at the tank a Hi-Low type? a big mix valve with a smaller one attached. To get accurate temperature at low flows you need a 1/2 or 3/4 valve, and the larger one for all fixtures flowing.
Could be the recirc loop has balancing valves that were never adjusted also?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
The hospital I speak of has 2 eye wash/showers, they are suppose to have mix valves, 1 is above the ceiling, the other in a flush wall box with door.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements