Concerns about recent boiler installation

Options
2»

Comments

  • NY_Rob
    NY_Rob Member Posts: 1,370
    edited November 2017
    Options
    Some of the PVC manufacturers acknowledge that their D1785/D2665 is being used in exhaust systems and offer guidelines for use....

    https://www.northamericanpipe.com/sites/default/files/PL-PS-001_0117_D1785-D2665-1.pdf


  • Steamhead
    Steamhead Member Posts: 16,845
    Options
    There are better plastic venting systems that are UL approved. It's time to ban PVC for venting.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Solid_Fuel_Man
    Solid_Fuel_Man Member Posts: 2,646
    Options
    Here in Maine it is the same way. If the manufacturer states that PVC is an approved venting material then we are free to use it. That said 99% of the installs I see use PVC. The only place I don't see PVC is when the manufacturer doesn't allow for it in the I&O (Viessmann).

    Our industry won't make the change until we are convinced that PVC is an actual hazard. The chloride alone running back into the boiler is enough for me to use PP, but PVC glues up nice and is always on the truck....
    Serving Northern Maine HVAC & Controls. I burn wood, it smells good!
  • wklopf
    wklopf Member Posts: 44
    Options
    KC_Jones said:

    Here is a direct quote from D1785

    “This standard specification for PVC pipe does not include requirements for pipe and fittings intended to be used to vent combustion gases."

    I found this on the Charlotte pipe site.

    "As stated in the
    International Code Council’s International Fuel Gas Code
    503.4.1.1:
    Plastic Pipe and fittings used to vent appliances shall be
    installed in accordance with the appliance manufacturer’s
    installation instructions."

    The HTP installation instructions clearly state that PVC pipe meeting ASTM standard D1785 is acceptable. However, I am wondering about another thing. The HTP instructions say that a 2" 90 is equivalent to 8' of straight pipe and a 3" 90 is equivalent to 5' of straight pipe. However, the Charlotte pipe site has a table which states that a 2" 90 degree elbow has a friction loss equivalent to 5.7' of straight pipe, while for 3" pipe the number is 7.9'. Is it possible that HTP got it backwards in their directions?

  • KC_Jones
    KC_Jones Member Posts: 5,739
    Options
    Your quote states plastic pipe, not PVC. There are plastic pipes that are specifically designed for use in venting that aren't made out of PVC.

    If you read carefully the boiler manufacturer says to use a product that meets a standard for venting. That standard states it isn't for venting and the pipe manufacturer says follow what the boiler manufacturer says.

    This is a very elaborate CYA so no one takes responsibility.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • wklopf
    wklopf Member Posts: 44
    Options
    I did a search on Google for plastic pipe for boiler exhaust and found the following piece which suggests using CPVC for the exhaust vent, due to its higher temperature resistance.

    https://www.thespruce.com/vent-pipes-high-efficiency-condensing-furnaces-4119901
  • wklopf
    wklopf Member Posts: 44
    Options
    After reading the piece below, I'm beginning to think that stainless steel is the only safe material for exhaust vents.

    https://www.phcppros.com/articles/1911-is-pvc-an-acceptable-vent-material-for-flue-gases
  • Leon82
    Leon82 Member Posts: 684
    Options
    Polypropylene is also available, but it costs more.
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,545
    Options
    @wklopf the difference in fitting resistance is always an issue. With plastic pipe it could be the difference between drainage or long radius elbows versus pressure or short radius elbows.

    Black fittings are ridiculous , you can look up 5 different charts and get 5 different answers for the same fittings
  • wklopf
    wklopf Member Posts: 44
    Options
    After studying the situation, I'm going to get the intake replaced with 3" PVC and the exhaust replaced with 3" polypropylene. That way, the effective length will be under the max of 100' for 3" pipes.