PressureTrol setting
richarddowling
Member Posts: 28
I have cut-in type control. I am reading in Dan's book that cut in should be set at 1/2 psig. Is that .5 on my control? Looks like wheel is set a 1 psig.
0
Comments
-
Yes, .5 on the front scale0
-
here is a picture of my control for my 2 pipe steam system. If I set it a .5 does that create more pressure, or is that controlled by the inside dial?0
-
You should set it just a bit above 0.5 -- putting it all the way down can let the linkage inside disengage, which is a nuisance. Then the inside dial -- which should be set at 1 -- will determine where it cuts out (the cutout pressure is the sum of the outside dial and the inside dial).
And remember: the pressuretrol does not create pressure, it simply controls it so it doesn't get too high. What creates pressure is the boiling water in the boiler. There are many factors which combine to determine just how much pressure the boiling will create -- venting, size of system, running time, room temperatures, etc.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thanks Jamie. How can I be sure dial inside is set properly? Is there a marking?0
-
Yes there is. Should be set at 1.richarddowling said:Thanks Jamie. How can I be sure dial inside is set properly? Is there a marking?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
A lot of these Pressuretrols don't have an arrow or tick mark on them. To set it at "1" turn the wheel until the "1" is facing out (to the front of the Pressuretrol.0
-
I found a tick mark. it was behind one of the wires. It was set at one. Thanks !!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements