I'm having problems with my columbia boiler and it appears to be in the lwco. It is a warrick 26c1c0. The problem is it has no voltage output on the NO terminal. My question is, Does anyone know for sure the voltage on the NO spade. Is it 12vdc or 120ac. spec sheet doesnt show anything

Comments

  • ratio
    ratio Member Posts: 3,774
    Check the voltage across the contacts, C to NO. If you show ≈0 volts the contacts are closed. If you see a nominal 24 or 120 volts that's your control voltage & the contacts are open. If you see something oddball the contacts aren't making cleanly.