My Story - Saving another steam system
Comments
-
I have 1x Gorton 2, a big mouth and 2 Gorton 1's to maximize the 3/4" tapping. Plus 2 more varivents on the main, and 1 varivent about 5' down above the first elbow on longest runout to the master bedroom.gfrbrookline said:All of my main vents are on antlers off of a 3/4 fitting, worked wonders.
I would suggest either ventrite #1 or Hoffman 1A vents for the rads. They can easily be adjusted so you can fine tune all of the rads. I tried the Gorton and Mom but wasn't thrilled.
I have 1A's on 3 radiators, 1 ventrite, and mix of Gortons and Maid-o-Mist, 2 Hoffman 40's and 2 varivents at the very end.
The challenge is a 1A only have a range between approx. a #5 - #6. Ventrite, between a #4 - #5. A Hoffman 40 it right between a 4 & 5 and I have a bunch of those I pulled off.
In my "inventory", I also have:
1) A TON of Gorton C's and D's.
2) couple 70A Airports which are obsolete, but just slightly larger than a 40.
3) A old Riselt #2? I think it says. It's a 2 piece assembly, solid brass. No idea what it's venting rate is. It still works. It was mounted to a radiator that was laying by a shed out back. Probably was used as a replacement at some point in the 40's I'd guess. Probably a non vacuum vent and replaced a failing #2.
4) 1 working Hoffman #2 vacuum vent that ironically was on the largest radiator. BUT, wondering if a vacuum vent almost works better on a larger radiator like that. I might install it on a very small entry way radiator in my entry way.
Just have to keep fiddling with it to get it all balanced.0 -
Quick Update:
Replace 1/2 the vents with Ventrites and Gorton/MoM 4's plus a really old cute little vent I found on a radiator that was laying out back behind the shed. I think it's from the 30's. Heavy, solid brass, 2 piece threaded together I assume has an alcohol filled float like a Hoffman 40. Slowed everything down and it's working well.
Added more main venting by tapping a couple more 1/4" holes and using some extra Varivents I had. I removed all the insulation on the dry return header after the last run out. Wanted a little more heat in the basement there anyway. Warms the kitchen, foyer and dining room floors a little, which is nice. Discovered a galvanized elbow and the 2-1/2" union is galvanized. So i can see where the boiler replacement started.
I have things pretty well balanced, heating up at the same time. Minimal noise on vents.
Still have some whistling on shutdown after a longer run as steam collapses to vacuum. Adding more main venting helped a little but didn't fix it. Almost tempted to add a small vacuum breaker on it to to quiet it. Fortunately it doesn't do it on the upstairs radiators. Of course, the system originall have Hoffman #2's (still have 1 I took off one radiator) and probably a 76 or 11 on the main. With a slightly smaller boiler, it would work really well I think.
Still having issues with the autofill on both LWCO, it overfilled the boiler yesterday, but the vaporstat prevents it from firing when flooded.
Operating numbers:
Main venting phase: <0.5-0.9oz (5 minutes from a warm (but not hot) start. Haven't timed a hot start but i suspect it's under 2 minutes.
Heating phase: 1-1.5oz. Vaprostat set at 4oz. pressure doensn't build until all radiators are filled.
Boiler size: 375k input (300k nameplate output)
EDR: 710
I think a 275k would be about right a 250 might work well too if I slow the venting down even more.
Question, will the big mouth vent, if still hot, open under vacuum?
0 -
why not just install a 1/2 or 3/4 inch check valve as a vacuum breaker if the noise is a problem0
-
I think i might. Good idea. Could just add it to the end of the main vent tree. Will obviously need to make sure its rated for at least 240F max.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements