Will a Flow Restrictor solve my problem
Joseph_4
Member Posts: 293
Hi.
I have a customer with an oil fired boiler with a domestic coil. They have complaints that shower not maintaining temp. properly. I went to the property and see that it stays on a comfortable temperature for about 2 to 3 minutes, After that, I then needed to turn it further in the hot setting to get it comfortable again. Otherwise it is already somewhat cold. and this continues like this.
Would a flow restrictor on coil help them have a more steady shower?
Thanks
Joe
HHI Services LLC
I have a customer with an oil fired boiler with a domestic coil. They have complaints that shower not maintaining temp. properly. I went to the property and see that it stays on a comfortable temperature for about 2 to 3 minutes, After that, I then needed to turn it further in the hot setting to get it comfortable again. Otherwise it is already somewhat cold. and this continues like this.
Would a flow restrictor on coil help them have a more steady shower?
Thanks
Joe
HHI Services LLC
0
Comments
-
The domestic coil may need to be flushed. If you look at the manufacturer ratings, they should tell you how many gpm of hot water it will produce.0
-
A flow restrictor will probably help but we need more information:
Steam or water boiler
If steam is the boiler water level covering the tankless coil
The coil may need cleaning as @Harvey Ramer said
what temperature is your boiler water
does the coil have a mixing valve and is it working properly0 -
As @Harvey Ramer and @EBEBRATT-Ed have noted -- if it worked some time ago, but not now, I'd bet on the coil needing to be cleaned. Either inside or outside -- or both.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Hi,
It its a steam boiler and coiler definitely not totally covered. Not a proper mixing valve. .. He has multiple tenants and just bought property... I know I'm jumping ...would he be best off with a booster tank.. or do you all think we could get coil to do job for his multiple showers?
Has like 4 to 5 showers.
Thanks
Joe0 -
Look into adding an indirect or another type of hot water heater.
A tankless coil will not satisfy multiple tennants0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 421 Carbon Monoxide Awareness
- 81 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 893 Plumbing
- 5.9K Radiant Heating
- 379 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements